I put C3 and i believe it is a C3 in the napit book.Agree with you there thats always a code 3 for me
Discuss Poor install EICR 12 year old hotel in the Electrical Forum area at ElectriciansForums.net
I put C3 and i believe it is a C3 in the napit book.Agree with you there thats always a code 3 for me
There is no right or wrong answer its down to the persifics of each situation and you make a judgment call on it I will stick with my code 3 but would not judge someone else if they where to code 2 it .Again reading the napit codebreakers book it states holes not made goot as to reduce the spread of fire are C2. I would rather C2 and have a valid reference such as a book than to C3 it and argue against it.
The sockets are not labelled, no risk assessment and they are not being used for the fridges in alot of the rooms. The client also said that he often finds the fridges have been unplugged as there isnt enough sockets in the roomsThe idea is tho that you are now outside the equipotential bonding using outdoor equipment so I’d agree that if socket outlets that are not likely to be used outdoors and this is carefull considered by the inspector perhaps in conjunction with the client, then I agree a C3 at worst for no rcd protection to sockets.
You are coding against additional protection to the user and not the equipment plugged into it
For a specific socket used as in the op for a fridge it can’t possibly be a C2 code
Cant see above the DB to see if its cleated well and they all seam to be coming in at angles. Its all together rough so ill stick with C2. If i was to share some of the communal areas you would agree. The rooms are good compared.If the swa is glanded at the supply end and the armour is at least connected to earth, I can’t see how it can possibly be a C2 unless there is signs of mechanical stresses on the cable at the load end?
I think youd agree that it is rough and would prefer to see the DB installed properly and stick an rcd socket on the socket not protected as again the client has stated people unplug the fridge and use it for all sorts.There is no right or wrong answer its down to the persifics of each situation and you make a judgment call on it I will stick with my code 3 but would not judge someone else if they where to code 2 it .
Yes its classed as commercial premesis.Does it give a reason for this? , also is a hotel classed as commercial I thought they would be classed as simply a hotel
But the reg 411.3.3 specifically says risk assessment required and even if ther was its clearly not being used for a specific item of equipment. I still think C2 when the public are involved especially in terms of liability.Regarding the socket, it's a code 3 for me, however in these circumstances I always add an advisory note that the provision of RCD protection is strongly recommended. Given that under a very recent edition of Bs7671 the provision of a socket outlet for a specific item of equipment was permitted without RCD protection it is very hard to justify a 'potentially dangerous' code.
Risk assessments are not out of the window on non domestic installations 411.3.3 an exception to (i) is permitted where other than an installation in a dwelling, a documented risk assessment determines that rcd protection is not necessaryIt’s the 18th now.
All socket-outlets must have RCD protection.
Risk Assessments are out the window.
The regulations do not differ on who is using the sockets so you can’t make that argumentBut the reg 411.3.3 specifically says risk assessment required and even if ther was its clearly not being used for a specific item of equipment. I still think C2 when the public are involved especially in terms of liability.
The regulations do not differ on who is using the sockets so you can’t make that argumentBut the reg 411.3.3 specifically says risk assessment required and even if ther was its clearly not being used for a specific item of equipment. I still think C2 when the public are involved especially in terms of liability.
they do and can not speak for the whole industry.
I disagree on the relaxation. Its always been for specific use items and in this instance the socket has extention leads plugged in etc. The hotel would be liable in my eyes. You can make the argument as in my eyes the reg does differ from the users when it specifically says risk assessment to be performed in non dwelling etc...
I stand corrected, thought that was being dropped.Risk assessments are not out of the window on non domestic installations 411.3.3 an exception to (i) is permitted where other than an installation in a dwelling, a documented risk assessment determines that rcd protection is not necessary