There is a fuse spur switch from the ring main, this spur feeds a two double sockets as a radial to the shed, is on 2.5mm flex in conduit underground. (Installed by Council Electrician)
What I want to know is; can I use the fused spur to power a CU and run a lighting circuit as well as a ring main/radial from this in the shed?
Wasn't sure if I could change the 2.5mm flex to a 4mm or 6mm as main power to CU (40A main breaker?) And run a 32A ring main/20or16A radial circuit and a 6A lighting circuit.
But then was wondering if I can do i need to up the fuse size in the spur? Its physically impossible to run a new cable from the existing CU in the house...
Long story short; I would like lights included in the shed, and want to know if I can use the fuse spur to power a CU to run my circuits from.
I thought spurring from a spur was bad practice? Regardless of them both being fused? Didn't think to mention it due to this?
A spur only applies to a ring final circuit and yes you cannot spur from an unfused spur- but in this case, the spur is a fused connection unit and you can branch off as many times as you like without overloading the cable due to the 13A fuse.
If it was a radial circuit, then the concept of a spur doesn't really exist and you can branch off in any direction from any point.
Essex
Other
If other, please explain
Apprenrice Maintenancd engineer Mechatronics pathway
Power to shed
UK
Sam2001,
telectrix,