Had a look at a job the other day, client has brought a MK RCD Garage CU and wants it connected up.
Supply is TNC-S with a 100mA RCCB protecting a BS1361 fuse board which has MCB's
Option 1. Replace the RCCB with a time delayed RCD and connect garage CU to new RCD
Option 2. Henley block the meter tails and connect both CU's to Henley block so both RCD's are in parallel
All wiring will be surface mounted SWA.
Both methods would achieve discrimination, which method would be the preferred one?
Supply is TNC-S with a 100mA RCCB protecting a BS1361 fuse board which has MCB's Are you sure this is a TNC-S system, if so why as it got this 100mA RCCB
Option 1. Replace the RCCB with a time delayed RCD and connect garage CU to new RCD Expensive.
Here is my take on things, Was the system originally TT and been converted to TNC-S and the RCCB never removed. If indeed it is a TNC-S, then, check your Ze reading and if it is a TNC-S then you can redesign your install
Thanks Malcolm
I did suspect it was a TT system but unable to find a connection to a earth rod. It looks like the electricity board converted to a TNC-S when they put a new meter in, they also changed tails to 25mm.
Tested the Ze, got a reading of 0.36 ohms :banghead: cleaned and tightened the contacts and got 0.35 ohms :cheesy: it's not ideal.
The RCCB is still operational.
Reply to Preferred method of installation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...