Hello all,

I’m now overthinking the - Prospective fault current test for the 2391 practical, the exam boards will be a 3 phase and a single phase board.

Do I test the three phase board and double the highest and use that for both DB’s or do I do one for 3 phase db1 and sep one for single phase db2
 
129EAEDF-A53C-47EF-8585-6963BF985CF0.jpeg
 
Test as close to the source as possible with parallel paths in place.

Test all three phases to earth then all three to neutral.

If your test meter is capable then test across all phases, L1 to L2, L2 to L3 then L2 to L3.

If you can’t test phase to phase then double the highest single phase measurement.

Do you know the difference between PSSC & PEFC?
 
Test as close to the source as possible with parallel paths in place.

Test all three phases to earth then all three to neutral.

If your test meter is capable then test across all phases, L1 to L2, L2 to L3 then L2 to L3.

If you can’t test phase to phase then double the highest single phase measurement.

Do you know the difference between PSSC & PEFC?
Yes I’m ok with that, Thank you
 
Prospective fault current at origin is the highest current, further into the installation the current will drop due to circuit resistances.
If the protective devices in the next DB are able to withstand the fault current at origin there is no need to measure again at the next DB because you already know they are OK.
 
Of course...

1) High reading on Main protective bonding conductor.

2) Low insulation resistance on the sub board / office board between neutral and earth.

3) No cpc continuity on the switch wire on one of the lights on a lighting circuit.

Also had a couple of high Zs readings due to poor connections and contact resistances.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Diver233

Arms
-
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Heavily Qualified Electrician / Teacher / Tutor - etc
Business Name
Lindum Fire Services ltd & www.zzeus.org.uk

Thread Information

Title
- Prospective fault current test 2391
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
Diver233,
Last reply from
ruston,
Replies
29
Views
4,142

Advert

Back
Top