looking at a job to do some bits- and rewire kitchen is on the to do list...

clients got me doubting myself now- even though I know I am right (well 99.98% now lol)

he wants the under unit points- isolation above at a central grid switch which is fair enough
so he went on to says 8way switch (4 switches and 4 fuses)

I told him you only need the dp switch for isolation purposes and the fuse is only needed to down rate if needed...

Was planning on running my ring through 4 of the dp switches (supply side)
and then spur off each dp switch in 2.5mm to the associated socket underneath (from load side)
and just have a dp switch AND grid spur for the the boiler- so just use a 5way grid (4x dp sw's and 1fuse)

spurring once off of the dp switch is no different from spurring once off of a outlet right...
 
Last edited:
Just make sure your back box is deep enough, as amlu said terminating 2.5 T&E is a right pain and you need lots of space behind!!
 
I have just done one and used fuses in the grid switch assembly, but I terminate into a connection plate behind the appliance rather than a socket and ahrd wire the appliance into that; then if the fuse does go I can easily replace it without dragging the associated appliance out or having to partially dismantle a built in appliance...my 2p worth...
 