sparkie-leeds

Hi All,

I am installing a rafiki 2 wire fire alarm system shortly, is it important to mark the cables going into the detector bases as "IN and OUT" or does it not matter with it been a 2 wire system.
 
As previously mentioned, ALLWAYS mark your line "in" at every point regardless of system type. Not only is it good practice but if a fault occurs it's so much easier to find by simply splitting the circuit and putting your eolr across the "in" leg.
Modern two wire and twinflex systems have the eol built into the detectors so the last point has to be set as "end of line" by using the dil switch.
You'll find that when you check the bases out, they are marked as IN+VE and OUT+VE with 0V being common so it is important to mark your lines.

rafiki.jpg
 
i just slap a bit of tape round the IN when 1st fixing.
 

Reply to Rafiki fire alarm in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
0
Views
627
Hi all, i'm just after a definitive answer regarding a fire alarm system in a communal area/stairwell. There are call points, smoke heads &...
Replies
4
Views
568
I'm installing mag-locks and fire door hold-open magnets at the moment and I'm wondering if any of the cable should be fire performance cable...
Replies
1
Views
582
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
251

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock