I am installing a rafiki 2 wire fire alarm system shortly, is it important to mark the cables going into the detector bases as "IN and OUT" or does it not matter with it been a 2 wire system.
 
i agree, but does it make a difference to the panel knowing which is in and out on a 2 wire system, i know conventional systems do
 
As previously mentioned, ALLWAYS mark your line "in" at every point regardless of system type. Not only is it good practice but if a fault occurs it's so much easier to find by simply splitting the circuit and putting your eolr across the "in" leg.
Modern two wire and twinflex systems have the eol built into the detectors so the last point has to be set as "end of line" by using the dil switch.
You'll find that when you check the bases out, they are marked as IN+VE and OUT+VE with 0V being common so it is important to mark your lines.

rafiki.jpg
 
i just slap a bit of tape round the IN when 1st fixing.
 
As mentioned it is good practice to mark them, from an electrical point of view however it makes absolutely no difference at all on Rafiki Twin system
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Rafiki fire alarm
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
sparkie-leeds,
Last reply from
TaffyDuck,
Replies
10
Views
1,585

Advert

Back
Top