Discuss RCBO Tripping. in the Australia area at ElectriciansForums.net
E
EoDM
Hi all i'm after a bit of advice. (2nd year apprentice..)
I recently done a bit of work in a flat and replaced the old fuse CU. The cable for the socket outlet that was supplying the boiler and the washing machine (which are in the bathroom, small flat) was just spared off from the ring main for the sockets.
So I disconnected the cable and pulled another in into the new CU and wired it into an B type 20amp 30ma RCBO.
When I came to turn on I checked the socket by plugging in the drill charger and it trips. I turned all other breakers off and tried again and still trips. I think it may be an earth fault? Not sure how i'd go about finding the fault that is causing it to trip.
Hope that all didn't sound to stupid and someone could give me some advice!?
Cheers
Hmm thanks, I will try it in the morning. But it's just the 1 run which is about 5 metres away of 2.5mm t&e going from the rcbo to the breaker, and the floorboards arn't back on yet so no nails etc could of pierced the cable or what have you.
I do you still have both the boiler and socket on the new run? If so does it only trip with the socket ? Also From what you are saying it only trips when you turn the socket on or when you plug something in regardless of switch position
The only thing on the run is the socket. Yeah it will trip only when the socket is switched on and that was with a drill battery charger and tried it with the boiler plugged in.
sounds like a neutral to earth fault to me ,disconnect the conductors and un plug the appliances and do a continuity test between the conductors and see if you have a reading if not then do an IR test , you say they are in the bathroom ,
I've checked my connections and the cable run. Although it wasnt't a new socket i was wiring into it was the existing but I have only visualy inspected it and it seems ok no damage.
As for the neutral there is only 1 bar on the consumer unit? and the neutral from the cable and the rcbo are both connected onto that. The FE is connected to the earth bar aswell.
Won't be able to preform any testing on it today on a different job! Thanks for all the replys aswell.
P.S on a brighter note passed my 2330 yesterday. Bring on next year! (thought i'd share that, ha)
Surely the neutral from your circuit should be connected into the RCBO not the neutral bar in the cu.
Sorry, yeah the neutral from the circuit IS connected into the rcbo and the rcbo neutral is connected into the neutral bar.
Reply to RCBO Tripping. in the Australia area at ElectriciansForums.net
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...