Rcbo keeps tripping when earth connected it is non earth rcbo. Have performed continuity test on wiring no fault on wiring any ideas ?
Circuit is 10a for exterior lighting although nothing connected yet want to sort out earth fault first. Supply is 3 phase tn-c
It is inside commercial db no rcd just mcb and rcbo mix 32 way db only one neutral and earth on each side. It trips even with no load when earth is connected no short found on continuity tests
Could also be live to earth fault!! Usually neutral to earth trips when pulling a load. Turn all other circuits off when trying to make sure.
Yes I.r test is required.
Test the rcd trip with an rcd tester!! X 0.5 shouldn't trip it.
Could also be live to earth fault!! Usually neutral to earth trips when pulling a load. Turn all other circuits off when trying to make sure.
Yes I.r test is required.
Test the rcd trip with an rcd tester!! X 0.5 shouldn't trip it.
Fair enough? I'm sure I had one tripping in the past when the load was pulled. Will this trip even though there are no other circuits connected? (Not saying your wrong)