Discuss rcbo tripping in the UK Electrical Forum area at ElectriciansForums.net

sajeel

-
Reaction score
49
Rcbo keeps tripping when earth connected it is non earth rcbo. Have performed continuity test on wiring no fault on wiring any ideas ?
Circuit is 10a for exterior lighting although nothing connected yet want to sort out earth fault first. Supply is 3 phase tn-c
 
It is inside commercial db no rcd just mcb and rcbo mix 32 way db only one neutral and earth on each side. It trips even with no load when earth is connected no short found on continuity tests
 
you need to do IR tests, not continuity. my guess is a N-E fault. if it's outside equipment suspect water ingress.
 
Could also be live to earth fault!! Usually neutral to earth trips when pulling a load. Turn all other circuits off when trying to make sure.
Yes I.r test is required.
Test the rcd trip with an rcd tester!! X 0.5 shouldn't trip it.
 
Could also be live to earth fault!! Usually neutral to earth trips when pulling a load. Turn all other circuits off when trying to make sure.
Yes I.r test is required.
Test the rcd trip with an rcd tester!! X 0.5 shouldn't trip it.

A neutral to earth fault/connection, will trip a connected RCD device, with or without an applied load!!
 
Fair enough? I'm sure I had one tripping in the past when the load was pulled. Will this trip even though there are no other circuits connected? (Not saying your wrong)
 

Reply to rcbo tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
891
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Replies
19
Views
2K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
Hi All, Seeking some thoughts on my own Omega free standing 900mm oven. Over the past year the oven has been tripping the supplying RCBO unit. I...
Replies
2
Views
505

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock