Rcbo keeps tripping when earth connected it is non earth rcbo. Have performed continuity test on wiring no fault on wiring any ideas ?
Circuit is 10a for exterior lighting although nothing connected yet want to sort out earth fault first. Supply is 3 phase tn-c
It is inside commercial db no rcd just mcb and rcbo mix 32 way db only one neutral and earth on each side. It trips even with no load when earth is connected no short found on continuity tests
you need to do IR tests, not continuity. my guess is a N-E fault. if it's outside equipment suspect water ingress.
Could also be live to earth fault!! Usually neutral to earth trips when pulling a load. Turn all other circuits off when trying to make sure.
Yes I.r test is required.
Test the rcd trip with an rcd tester!! X 0.5 shouldn't trip it.
A neutral to earth fault/connection, will trip a connected RCD device, with or without an applied load!!
Fair enough? I'm sure I had one tripping in the past when the load was pulled. Will this trip even though there are no other circuits connected? (Not saying your wrong)
Reply to rcbo tripping in the UK Electrical Forum area at ElectriciansForums.net
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Hi All, Seeking some thoughts on my own Omega free standing 900mm oven. Over the past year the oven has been tripping the supplying RCBO unit. I...