Discuss RCBO's on to old wiring....HELP!!! in the Industrial Electricians' Talk area at ElectriciansForums.net
S
sliver
I seem to be having alot of trouble after installing anew consumer unit with 5 RCBO's I have got really high milli second readings and dont understand why I am looking at 350 x 1 and no operation on x 5. IR is fine and so is R1 + R2. Any suggestions????:confused:
Check the size of your main MET and check your Ze if the main MET is to small or poor connection this will give you those sort of problems.
thanks for the reply mike. i've a rod which is installed beneath the lounge floor and am getting a reading of 56ohms .i've the possiblity of pme which will bring it down to 0.35,but am concerned that there may be a borrowed neutral on one of the old circuits,will this be a factor to effect newly installed circuits??
Borrowed neutral's usually take an RCD out as soon as you power up, have you tried swapping the Rcbo's around ( where the amps are the same ) to see if it's a duff rcbo?
Lee
thanks lee,i've got a problem that when the bathroom lighting is energised the rcbo trips out,so i think that is where the neutrel problem lies,but yes i,ve swaped ,and also installed other rcbo's to double check readings from the original onesand they come up with the same reading.thanks for the input the more views i can get on this the easier to solve for me
It probably is borrowed neutral. Some people have a habit of nicking the neutral from a shower feed to feed a light over the shower. If you have the choice of type of supply go for pme.
hi do you have up and down stairs lighting this seems to be the most likely
place to find borrowed neutral
Reply to RCBO's on to old wiring....HELP!!! in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...