sliver

I seem to be having alot of trouble after installing anew consumer unit with 5 RCBO's I have got really high milli second readings and dont understand why I am looking at 350 x 1 and no operation on x 5. IR is fine and so is R1 + R2. Any suggestions????:confused:
 
Check the size of your main MET and check your Ze if the main MET is to small or poor connection this will give you those sort of problems.
 
thanks for the reply mike. i've a rod which is installed beneath the lounge floor and am getting a reading of 56ohms .i've the possiblity of pme which will bring it down to 0.35,but am concerned that there may be a borrowed neutral on one of the old circuits,will this be a factor to effect newly installed circuits??
 
Borrowed neutral's usually take an RCD out as soon as you power up, have you tried swapping the Rcbo's around ( where the amps are the same ) to see if it's a duff rcbo?

Lee
 
thanks lee,i've got a problem that when the bathroom lighting is energised the rcbo trips out,so i think that is where the neutrel problem lies,but yes i,ve swaped ,and also installed other rcbo's to double check readings from the original onesand they come up with the same reading.thanks for the input the more views i can get on this the easier to solve for me
 
It probably is borrowed neutral. Some people have a habit of nicking the neutral from a shower feed to feed a light over the shower. If you have the choice of type of supply go for pme.
 
It probably is borrowed neutral. Some people have a habit of nicking the neutral from a shower feed to feed a light over the shower. If you have the choice of type of supply go for pme.
hi do you have up and down stairs lighting this seems to be the most likely
place to find borrowed neutral
 

Reply to RCBO's on to old wiring....HELP!!! in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock