Hi all,

I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.

If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?

Thanks
 
Should this question not be on the Screwfix forum ?

You would use a MCB. But do you know why ?
I would use an MCB as I believe there would be a level of RCD protection.

Obviously not the best situation as it would take out the whole consumer unit.

I've also read the affects of having an RCBO and RCD/RCCB together.

If I'm wrong, could you please explain?

Much appreciated
 
I would use an MCB as I believe there would be a level of RCD protection.

Obviously not the best situation as it would take out the whole consumer unit.

I've also read the affects of having an RCBO and RCD/RCCB together.



If I'm wrong, could you please explain?

Much appreciated

ideally, you'd upgrade the board to give circuit division between 2 RCDs or, better still, RCBOs. but you can only do as much as the customer is prepared to pay. in this case, a MCB for the new circuit is the most cost effective solution.
 
I would use an MCB as I believe there would be a level of RCD protection.

Obviously not the best situation as it would take out the whole consumer unit.

I've also read the affects of having an RCBO and RCD/RCCB together.

If I'm wrong, could you please explain?

Much appreciated

Your thinking along the correct lines. We're guessing to some degree as we don't know all the details but it seems ok.....if operation is satisfactory
 
It will have a 'S' in a square.

But it if this is installed this will not give your circuit appropriate RCD protection.

whole DB change is what I would recommend.
Thank you.

So if the customer would not pay for that, and it was a time delayed rccb, could a new circuit not have an rcbo so it is protected?
 

Reply to RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock