As I posted before, It may be a 30ma RCD upfront already, he has not stated rating.

I know but we were specifically talking about if the RCCB is time delayed. In this case it would not give his new circuit the required protection so a 30mA non time delayed RCBO will be required.
 
Yes Noob you should not have 2 of the same mA RCDs in line, unless your RCCB is 100mA & time delayed.
As you have not given a mA for the RCCB which would normally be on the front, are you mistaking it for a ELCB?
You may need to take a pic of it so members can check.
 
Yes you will need to RCBO it. If the main is time delayed you will achieve the required discrimination between the RCBO & the RCCB.

From the description , and without looking at it !
I would say that the installation is likely to be TT , hence the up front rcd ( probably an 100mA S type ) so why or how could it possibly be failing any regs if the new circuit was to be just installed on a new rcbo ( even then if needed ? ) , instead of a whole new board !?
 
It may well be one of these chuckle, and the OP is confused.
 

Attachments

  • CrabtreeELCB.jpg
    12.1 KB · Views: 74
From the description , and without looking at it !
I would say that the installation is likely to be TT , hence the up front rcd ( probably an 100mA S type ) so why or how could it possibly be failing any regs if the new circuit was to be just installed on a new rcbo ( even then if needed ? ) , instead of a whole new board !?

My point was the opposite. To not install a MCB but an RCBO.
 
My point was if he installs a new circuit to a board which has a RCD main switch (and doesn't need it) then in affect he will be making the existing circuits worse by adding to the problem of one RCD protecting the whole installation. I know it is not clear cut and is only my interpretation so I think a board change would ensure all the new work is compliant.
 
find me one!

I had this about 2 years ago , someone on here had found one on fleabay just to prove a point . :dunce2:
Despite it being from some knock off 3rd world importer , I still had to go to the trouble of explaining why it was as much use as ---- on a bull !
 

Reply to RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
452
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock