Hi all

I have seen a schematic drawing for a control panel recently where they (whoever drafted the drawings, designed the panel) show a RCD before the 230v/24v dc PSU, and the PSU is the only device downstream of the RCD

in my mind this has no merit. The 24v secondary d.c side of the PSU supplies electronic circuits

would you guys agree that the RCD is this instance serves no valuable function?

thanks
 
would you guys agree that the RCD is this instance serves no valuable function?
It depends, but in many cases no.

If the power supply has full safety separation (PELV, etc) then probably not, but it also might depend on any other risk factors that might impact on isolation: such as operating in an environment with the risk of water leaks, extreme condensation, or conductive dust, etc.

Also in might depend if the RCD is for the whole system and in a separate double-insulated box as it is part of TT earthing for the control panel, and serves to protect against cable damage on route to the PSU, etc.

TL;DR it needs a bit more context
 
It depends, but in many cases no.

If the power supply has full safety separation (PELV, etc) then probably not, but it also might depend on any other risk factors that might impact on isolation: such as operating in an environment with the risk of water leaks, extreme condensation, or conductive dust, etc.

Also in might depend if the RCD is for the whole system and in a separate double-insulated box as it is part of TT earthing for the control panel, and serves to protect against cable damage on route to the PSU, etc.

TL;DR it needs a bit more context
many thanks

the earthing system is TN-S

the RCD is inside the control panel and has only the 230v/24v PSU connected to it

my other thought is the RCD nuisance trips and then the 24v d.c is lost. There are solenoid valves, pressure sensors etc in this design along with PLC control for such sensors.

I just do not see the reason the placing an RCD at this location (electrically speaking)

thanks
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
dorset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Water Industry

Thread Information

Title
RCD before a 230v/24 PSU?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
bob6459,
Last reply from
bob6459,
Replies
2
Views
975

Advert