Hi Murdoch, looking at it, the swa comes from a protected circuit on the main house cu. This runs 150' to the end of the garden into the 6 way. SWA is earthed at house CU.

So you do have 2 RCD's in series then.

Time to get my coat
 
that's not the problem, but it's bad design as a fault on the sub-main circuits can cause the house RCD to trip, thus losing part of the house installation. i have had a similar fault caused by a N-E reversal in back of a socket outlet.
 
that's not the problem, but it's bad design as a fault on the sub-main circuits can cause the house RCD to trip, thus losing part of the house installation. i have had a similar fault caused by a N-E reversal in back of a socket outlet.
I can move the load to an unprotected side of the board.
 
that would eliminate the series RCDs. i think you need to look more closely at the garage installation for a fault once you have determined that you have a good RCD.
 
that would eliminate the series RCDs. i think you need to look more closely at the garage installation for a fault once you have determined that you have a good RCD.
Tomorrow I will power up the garage CU from an extension and see if this removes the fault.
 
Right I'm gonna suggest something that I may get screamed at for by some on here, I don't recommend doing it but as you have no test equip. It may be the only way to test (ish) an RCD. I would remove rcd from board, connect a flex with plug top on one end into the top L and N terminals and plug into working socket outlet in your house, then push test button, if it trips the rcd then you at least know it fuctions and its your wiring at fault.
 