No faulty unit tripped at 10mA after hitting Test Button - new unit tripping at 28mA

By the way this RCD was less than 6 months old!!!
I installed it last September - Ze 0.18 on a TN-S
 
no, will do that. RCD seems fine though. I'm gonna look into that earth reading from 1st floor sockets though, didnt get chance to yet
 
so..once youv sorted out your end to ends....you can just jolly well go round the points again on that circuit for a real value of (R1 R2)....cant you...

- - - Updated - - -

this is sounding more and more like the same old farce....
 
well i noticed the readings from 1st floor sockets were strange, and someone else pointed it out here just few mins ago....

L-L 0.79
N-N 0.79
E-E 0.52
 
well i noticed the readings from 1st floor sockets were strange, and someone else pointed it out here just few mins ago....

L-L 0.79
N-N 0.79
E-E 0.52


Those readings are R1, R2, Rn readings and they look fine to me!

R2 is 66% of R1/Rn
 
sorry mate, you must have joined us late. i already answered everything your asking in the first posts. RCD is setting, test button working, all circuits working fine. checked all connections, swapped RCD....
 