eh?.....I was looking at that aswell, didnt investigate, you think that has something to do with it? RCD should still trip on test right?
eh?.....I was looking at that aswell, didnt investigate, you think that has something to do with it? RCD should still trip on test right?
and what makes you think its the CPCs?no, will do that. RCD seems fine though. I'm gonna look into that earth reading from 1st floor sockets though, didnt get chance to yet
What is the Ze? Surely you got this reading first!no, will do that. RCD seems fine though. I'm gonna look into that earth reading from 1st floor sockets though, didnt get chance to yet
well i noticed the readings from 1st floor sockets were strange, and someone else pointed it out here just few mins ago....
L-L 0.79
N-N 0.79
E-E 0.52
eh?....try 1.67 for a 2.5/1.5...Those readings are R1, R2, Rn readings and they look fine to me!
R2 is 66% of R1/Rn
Those readings are R1, R2, Rn readings and they look fine to me!
R2 is 66% of R1/Rn
It is r1, r2 and rn for a start on the end to ends, and his r2 is lower than is r1 and rn, it should be 66% higher for 2.5/1.5 T&E
I'm guessing you mean that the Ze is 0.19. Can you set the RCD and does the test button work? I would now venture to suggest that the CPC has a voltage on it.0.19, already answered that