well the results from original RCD on DB1,

utility ring
times 1 - 27.2 ms
times 5 - 8.18 ms

downstairs sockets
times 1 - 27.4 ms
times 5 - 7.98

I didnt record the results after i swapped RCD, just that it did trip on test
 
why is there .79 on the live conductor end to ends and .52 end to end on the CPC on the first floor sockets?

- - - Updated - - -

and whats the Zdb?
 
I would like to think the OP has done a R1+R2 before energizing the DB,or is that asking for too much?
 
I was looking at that aswell, didnt investigate, you think that has something to do with it? RCD should still trip on test right?
 
I had this lastnight - went to a house - RCD tripping on split 2.
Tested split 1 and no trip upto 550mA

Hit the test button and then ramped it again - tripping at 10mA now - RCD replaced
 
I had this lastnight - went to a house - RCD tripping on split 2.
Tested split 1 and no trip upto 550mA

Hit the test button and then ramped it again - tripping at 10mA now - RCD replaced


Tripping at 10mA??
You sir have replaced a faulty RCD with another faulty RCD
Anyway to the op have you ramp tested the faulty RCD yet?
 