your thoughts just pulled in 6 4mm radials all enclosed in dado trunking all tests were ok rcd testing x half no trip on all 6 radials x1 tripped 29ms x5 tripped 29ms now i no these readings are all exceptable but found it a bit strange that it was 29ms for all circuts at x1 and x5 usually your x5 trips in about 8ms aslong as it trips in under 40ms its ok anyone had same
was that on auto test or manually setting the x1 and x5?
could be that when you switched to x5, you didn't click the switch in properly, or a meter fault. either way, i would retest, on auto ,i f your meter has this function.
I was testing hager RCBOs today - out of 10 x RcBOs 8 of them at x1 came back at between 8 and 9 ms and at x5 the same- seems v strange - awhich meter are you using is it the new megger>?
Seen this many a time and in some cases quicker @ x1 than x5. Wouldn't worry about it as long as they are within spec!
Yes yellow that's what readings I usually get with tester for my tests the meter has only just been calibrated I no there acceptable readings but just didn't seem right 29ms for all six circuits might retest tommorow
This is not unreasonable, most RCBOs use electronics to increase the sensitivity, speed and repeatability. This means there is often very little variation in speed of operation at x1 and x5, or between a batch of protective devices.
Where were you testing the RCD/RCBO, at the device terminals or at the socket outlets downstream??
All RCD devices should be tested at the device terminals for your recorded values, and not at the extremities of the circuit. The circuit will/should have already been tested/proved via ELI, Continuity, Polarity and IR tests etc...
You are therefore only testing the RCD devices themselves for conformity, not the wiring...
i checked at the sockets engineer54 i no you can check at rcd but its easier to just plug in at sockets rather than wrestle with leads and try an press test button with your nose ha ha i wouldnt of thought it would alter the readings or does it ive allways checked at sockets for rcd tests
that's not how we're taught at college........
Seems we have yet another collage lecturer teaching duff information to students!! This is getting to be a regular occurrence these day's!!!
Well i would suggest you get your lecturer to contact the manufacturers, who will all tell him to test RCD devices at the load terminals, and not at the circuit outlets!!
Nothing to stop you checking from circuit outlets, but not when your testing the device's trip/time parameters, when officially recording the results on report record sheets etc...
In his defence he is actually a good teacher and a lot better than most at the college. I think if you asked a lot of electricians they would test at the circuit outlets
No matter how good you are, you'll never know everything. Always learning.....