I have an rcd tripping. I have narrowed it down to one circuit from a spur isolator switch to a double socket that is floor mounted. By a process of elimination I have found that connecting just the live wire to the isolator switch causes the rcd trip. I though rcds were to do with neutral/earth problems.
I presume that I have some problem with the underfloor cable, but how can it trip the rcd?
 
Last edited by a moderator:
I have an rcd tripping. I have narrowed it down to one circuit from a spur isolator switch to a double socket that is floor mounted. By a process of elimination I have found that connecting just the live wire to the isolator switch causes the rcd trip. I though rcds were to do with neutral/earth problems.
I presume that I have some problem with the underfloor cable, but how can it trip the rcd?
Yes, RCDs will trip in response to neutral-earth faults, but if that were all they did then they wouldn't be any use for protection against shock. They trip just as often in response to line-earth* faults and thus protect a victim in contact with only the line conductor — plus a stray conductive path to earth.

* I'm not keen on the word 'live' used in this way & neither is BS7671; it defines 'live' differently.)

The fault could be in the underfloor cable, but doesn't have to be. Start by taking the socket out of its back-box and check that the wiring has no damaged insulation or accidental contact with the box or other metal & that the polarity (L & N) at the socket is correct. If it is, measure the resistance between L & E (both at the isolator end) with a suitable low-range meter. That will give a clue to the position of the fault. The reading is likely to be very low (< 1Ω).

Assuming the spur is wired with 2.5 mm² copper cable, the resistance of the line or neutral conductors is 6.8 mΩ per metre, and the (thinner) earth conductor is 17 mΩ per metre.
 
Presumably you have unplugged what was in the floor socket and it still trips?
As post #2, it the fault could be within the double socket or the switch fused isolating unit and not necessarily the cable under the floor.
Isolate the circuit first before checking. Sometimes a 'chaffed' cable by the accessory fixing screw for example can take years to 'break down' and cause a problem.
Any evidence of vermin (assuming void under floor) as that is most likely cause.
Unless access to and competent with electrical test equipment, testing as per post#2 should be left to a qualified electrician.
 
Presumably you have unplugged what was in the floor socket and it still trips?
As post #2, it the fault could be within the double socket or the switch fused isolating unit and not necessarily the cable under the floor.
Isolate the circuit first before checking. Sometimes a 'chaffed' cable by the accessory fixing screw for example can take years to 'break down' and cause a problem.
Any evidence of vermin (assuming void under floor) as that is most likely cause.
Unless access to and competent with electrical test equipment, testing as per post#2 should be left to a qualified electrician.
I have now established that the three wires in the underfloor cable are not shorting to each other. It is only connecting the live wire to the isolating switch that causes the rcd to trip so I presume that the live wire is exposed in some way under the floor(in solid cement) and is earthing itself to the surroundings.

Robin Madge
 
I have now established that the three wires in the underfloor cable are not shorting to each other.
How did you establish that, with an Insulation Test Meter? (A multi meter is unlikely to provide an adequate test).
It is only connecting the live wire to the isolating switch that causes the rcd to trip
So 'downstream' from the isolating switch, under the screed? so could still be the cable? Have you isolated the 3ends of the cable within the floor socket (ie removed the floor socket to eliminate that as being the cause)?

If in screed, unlikely to be vermin, maybe cable was damaged when first installed?
 
How did you establish that, with an Insulation Test Meter? (A multi meter is unlikely to provide an adequate test).

So 'downstream' from the isolating switch, under the screed? so could still be the cable? Have you isolated the 3ends of the cable within the floor socket (ie removed the floor socket to eliminate that as being the cause)?

If in screed, unlikely to be vermin, maybe cable was damaged when first installed?
Might be a long term problem that has got worse. Had a trip a few weeks ago that reset OK, now is continuous and won't reset. Cable has been in place for about 12 years. Definitely the live wire in the cable causing it. I shall have either dig up the floor(tiled) or set up a new route!
 
The isolator probably switches the live and neutral so the fault could be either. Needs correct testing.
 
The isolator probably switches the live and neutral so the fault could be either. Needs correct testing.
I have tried various combinations of connecting the wires from the cable to the isolator. The only thing that trips the circuit is attaching the live wire, even just the live wire. The live wire is not shorting through to either of the other wires and they are all not connected to the floor socket or anything else, insulated ends. Therefore problem is with the live wire in the cable somewhere in the cemented floor.
 
I have an rcd tripping. I have narrowed it down to one circuit from a spur isolator switch to a double socket that is floor mounted. By a process of elimination I have found that connecting just the live wire to the isolator switch causes the rcd trip. I though rcds were to do with neutral/earth problems.
I presume that I have some problem with the underfloor cable, but how can it trip the rcd?
Because that is what it is designed to do, among other things. I am not in favour of DIY people messing around with electrical safety devices that is how we get people killed. Please get a competent electrician to check out your property.
 