Is there one certain item that trips is?
IR between the RFC Neutral and all other Neutrals to eliminate a borrowed neutral
Whats the IR for N/E and L/E
Is it one certain socket that trips the RCD?
What board did you have installed before?
 
Do you mean every circuit is disconnected or just the RFC's ?, I am not sure what you mean here.

Have you checked the factory fitted split load connections ?, I have had the odd CU miswired from new before.


I take it from the reply that the only cct left connected was the faulted one and all the neutrals were out as well!
 
Is there one certain item that trips is?
IR between the RFC Neutral and all other Neutrals to eliminate a borrowed neutral
Whats the IR for N/E and L/E
Is it one certain socket that trips the RCD?

What board did you have installed before?

I was going to say exactly the same as you Nicholas, as I have had a diy extension joining the two ring circuits before, which is why I asked the OP to clarify his earlier remarks about disconnecting everthing.
 
Do you mean every circuit is disconnected or just the RFC's ?, I am not sure what you mean here.

Have you checked the factory fitted split load connections ?, I have had the odd CU miswired from new before.

I removed all other neutrals from both nuetral bars and left just the rfc connected and the RCD still tripped, if I connect lighting circuit onto same rcd it holds with rfc connected but no appliances on, turn on an appliance and it trips.
 
When you disconnected all Neutrals (stupid question) did you isolate all Lines - as in turn all MCBs off?

When you say you put light neutral back in it held - is the lighting on same RCD as the FRC?

- - - Updated - - -

Is it a split load board?

He said it is in the OP
 
See Nicholas's and my post just above, disconnect everything and re-check your end to ends on the RFC's, double check that you have not cross connected anything, ie. correct Neutrals matched to correct L's and in the correct bars for the correct RCD, and also IR test between both circuits L and N to L and N of the other RFC, as Nicholas has suggested,
 
Last edited by a moderator:
See Nicholas's and my post just above, disconnect everything and re-check your end to ends on the RFC's, double check that you have not cross connected anything, ie. correct Neutrals matched to correct L's and in the correct bars for the correct RCD, and also IR test between both circuits L and N to L and N of the other RFC, as Nicholas has suggested,

I have checked for cross connections and have tried with the rfc as the only circuit connected to the board, still trips
 
Hi mate,

Start at the beginning, check your continuities, then IR tests, then fit one ring final circuit to the board, and let us know what is happening, do not miss a step.
 
I agree with the advice you have been given so far, in particular IR between the RFC neutrals and cpc and line/cpcs as well as check all connections (board and RFC) for tightness. This kind of problem can give you a sore head and you begin to tie yourself in knots. Step by step, break it down and you'll find the problem.
Regards.
 
There is only 1 rfc
still start at the beginning, do your end to end continuities your cross connection (R1 +R2) test, then the IR test, and connect only that circuit to the board, as I said don't be tempted to miss a step, post your readings and let us know what is happening.

Also try to post a photo of the boards internals, and we will try to help you.
 
If the RCD is tripping after you have plugged one thing in (and turned it on) then its a borrowed neutral or incorrectly wired CU.
If the RCD trips after the 10th item and on the same item each time then its the appliance!

If the RCD wont hold when everything is unplugged you have hashed up!


You only posted one IR reading - that is that IR reading?? L-N, N-E or L-E?? all different so dont just test L&N-E.

Rip the RFC out of the CU and IR between both N bars when everything else is wired in.

Dont plug anything in until you get the both RCDs holding!
 
Thanks guys for all your suggestions, as Polo1 has said sometimes these things can give you a sore head and I had started to think I had done something wrong. I'll go back and start with the basics,check all connections and hopefully I'll find the fault.
 
Thanks guys for all your suggestions, as Polo1 has said sometimes these things can give you a sore head and I had started to think I had done something wrong. I'll go back and start with the basics,check all connections and hopefully I'll find the fault.

....and remember to tell us what the problem was!
 