Has anyone got any experience of wiring these? I have been asked to wire up 6 hook up points for Thermo King refrigerated container lorries. They have a start up current of 70A and full load current of 17A. There is an existing 3 phase distribution board with one 3 phase way left on it. I was hoping to use this spare way to feed a seperate consumer unit for the 6 container circuits. The cable run is about 50m and am wondering if anyone has any suggestions?
 
These hook up points will be mounted on a concrete wall outside and wired in SWA. Will i need to wire a starter or anything to account for the high start up load?
 
cable size will require to be worked out length ect ect As for sockets they were MK Commando interlocked each had seperate circuit
 
at my sub DB is it fine to just have a 125A 4 pole incomer and then 32a 3 pole MCB's type D for each circuit? RCD protection is not required I believe.
 
RCD protection may not be required but I personally would fit it. The trailer cables can get in a bit of a state, wagon drivers aren’t noted for being delicate.
 
that was one of the regular jobs at depot we maintained "Check trailer leads faulty" should have read"Check trailer leads run over driven away without unplugging and generaly abused !" the leads we used were made up of SY Cable and withstood a fair bit but deffo fit RCDsS either in db or rcd commando sockets
 
Silly question, but do the lorries require single phase or 3 phase power (220V or 415V) ?

I would also agree with the fitting of RCD/RCBO type sockets. Classing your drivers as "trained personell" and training them in the proper use of the sockets / plugs would also mean that you can get away with 100mA RCDs which may eliminate nuisance tripping found on 30mA RCDs with startup currents. My reasoning being that a wagon is "portable equipment" that could be expected to be towed away with the plug still attached !
 
When ordering the new equipment add spare pugs and sockets. Keep in mind whatever you do, the drivers will find a way of wrecking it!
With regard to the type of socket, these trailers will be used at other depots so be sure as to the type you fit.

When positioning the sockets be sure they’re out of harms way. 38T wagon Vs commando socket = No Contest!

There was a post on here a while ago started by a wagon driver, it made good reading.
 
Last edited by a moderator:
What happens with respect to phase rotation?

Is there a device on the fridge system that ensures correct rotation?

Irrelevant response to OP's question... but just thought I'd ask.
 
Last edited by a moderator:
I have seen 3 phase plugs that come with 2 of the phase pins on a rotatable swivel, so you can swap the rotation without disconecting wires or opening panels/DBs up. Id like to think that such an expensive piece of kit as a refrigerated wagon has some form of correct phase detection in it - The A60 pressurised cabs we get offshore all have an indication of correct or wrong phasing. If its wrong then the supply panel is locked out until you correct it
 
Last edited:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South Wales

Thread Information

Title
Refrigerated lorry hook up points
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
slocm3105,
Last reply from
Knobhead,
Replies
18
Views
11,284

Advert

Back
Top