I have been asked to change a consumer unit with a dual supply. I have a common supply, an off peak supply and one neutral, all 16mm double insulated tails. The current set up has the neutral running to the first isolator and then looping from there to the off peak isolator (2 16mm tails in the same terminal).
I'm not sure I would be happy running the neutral in the same manner in a new consumer unit (Please tell me if I'm being overly cautious. Most isolators have cage clamp terminals so may well be fine) so was wondering if anyone knew of an off the shelf solution to install. I'm thinking something that would maybe allow me tee off from a dedicated neutral bar with a couple of cables, each with there own separate terminal. Oh and it has to be no more than 200mm tall as it is going above the front door! (gotta love the wisdom of flat designs back in the day!). The only thing that has come to mind so far is getting a split load board and installing 2 isolators, RCBO's and using the usual high integrity neutral bar to split the incoming neutral (I wall assume my position in front of the firing squad if that one is way off the mark!)
Your help is very much appreciated
Where does the single neutral originate, Dual rate meter or 2 separate meters or Henley or Cut-out or ??
It comes from a digital eco 7 meter in a Mantel unit in the hall outside the flat. There is a neutral from the cut out to the meter and one neutral exiting on the way to the consumer unit. I'm not sure I'd be allow to run a secondary neutral in trunking out in to the hall as that's the freehold's manor!
True, but typically they have clamp connections that take 35mm cable so would be no problem for 2 * 16mm.
You could use a Henley block to split them first, then the 4-p isolator so both supplies (and related neutrals) go off in one go.
Probably could get a 4-p switch for the CU but might need to check with the manufacturer (unless they list one) to be sure it is compatible with any internal bus bar arrangements.
Also have the added annoyance of the meter being separate from the flat and in the communal area of the flats. I would need to get the ok from the freehold to start screwing up trunking in the hall and running cables. Maybe that would be the way to go. Freeholds are rarely helpful in my experience!