Hi guys

doing a ring continuity test . R1,Rn,R2 values all okay. Done figure of 8. Tested at each point and not allowing continuity test due to 8 volts. Stuck on what this is? Any ideas ?
 
Is anything else on within the building?

It could be induced current from a different circuit.
Drop the power to the whole property and see if it disapears
 
Do a walk around and visually check that everything is off, I have been into houses before and someone has Henley blocked before the meter to another CU.
Other option is they borrowed a supply from next door.

Saying that I was at a house last week, CU change - up in the attic was 2 rings. One for the house I was working on and 1 for next door.

It turned out the attic wall as 2ft over next door instead of directly over the separating wall
 
Hi guys

doing a ring continuity test . R1,Rn,R2 values all okay. Done figure of 8. Tested at each point and not allowing continuity test due to 8 volts. Stuck on what this is? Any ideas ?

r1 r2 and rn you mean I hope
 