sparky928

Had a call this Morning that her rcd keeps tripping.


So i went round there First of all unplugged everything still tripping. Done a few tests L-E N-E L-N and end to end test all came back as 0 mohms.

So i Separated the legs at both the board and the sockets found the fault leg.

Reconnected the good leg got a good part of the sockets working.
So i went upstairs as the cables are coming down to the sockets and the room above is the bathroom with vinyl flooring. She didnt want me to the lift the floor up without speaking to her husband.
.
And then the customer tells me that a few months back they had a leak in the bathroom.

i was thinking water probably got in the junction box.

By why didnt it trip a few months back?
 
I would find the joist run direction and take a board up in an adjacent room to see if you can see across under the bathroom.. the actual fault may not be under the bathroom, it may just seem its likely to be there. Also see if the bath panel comes off and you have access under the floor beneath the bath.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring Main fault
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
sparky928,
Last reply from
Darkwood,
Replies
6
Views
1,408

Advert

Back
Top