If that is how you think the ring is faulty then run a cable from socket two to socket five and disconnect the potentially faulty legs. The ring should then test as a no fault ring and if you do a full ring test then you can ensure that other sockets suspected to be OK are in fact on this reduced ring.

Then you can concentrate your fault finding on the suspect cables and ignore the rest.
 
Also there is a lot of moisture in the air (due to urine and no windows open)

Moisture alone will not give you a reading of 1.4kΩ unless the whole circuit is underwater. 1.4MΩ yes, but not 1.4kΩ. If that reading is correct, then there must be some other mechanism, such as a 'contaminated' fitting that has tracked, carbonised and is now a charred heap of stuff instead of a plastic accessory. You mention sparks and bangs - where from? If from the DB, then probably the MCB was reacting to a hard short and the 1.4k is what's left now the fault has burnt itself out. One way or another it ought to be visible when you reach it.
 
I've kinda sorted it. Now able to get into bedroom 1, I found the insulation fault between sockets 3 & 4. It was in the stretch between socket 4 and about a foot under the floor. I was unable to see any reasons (nails, backbox hole rubbing etc) suggesting a breakdown within the cable so I just cut both legs below the floor, joined them and bypassed the socket. THEN, I found another fault on the same circuit in the kitchen between new found socket (opposite to socket 6) and the ccu. As I couldn't get into bedroom 3 to locate the fault I split the ring at that point, did all the testing which was good, downgraded the MCB and made the ring into a radial. I suggested she call me when she's cleared the room.

I actually also found an earth fault to the fluorescent in the kitchen but thats another story..
I also told her she could do with a rewire... and a tidy up...
 