Hi All,

Will post an introduction on the new members forum but need to blurt out my question while its still in my head.

Me and Mrs JimmyB1988 have moved into our first house, it has a split consumer unit, half on RCD half not, my sockets were on the half without an RCD. One breaker does all the sockets including the Kitchen. So I moved the sockets breaker over to the RCD side, moved the neutrals too over to the RCD neutral bar. But it keeps tripping the RCD, all works fine on non protected side, i insulation resistance tested the circuit and reads 0Mohms between line + neutral, neutral + earth, line + earth? Confused?
icon9.png


Can anyone think of anything obvious?

Thanks Guys/Girls
icon7.png
 
Hi,
Firstly I see your qualifications are in Engineering, although you may have electrical experience.
You need to double check the cables you have moved across are definitely the Line Neutral & EARTH for that circuit.
Secondly , unplug everything from the Ring Main to check whether it may be an appliance fault.
Finally, If you are using an IR tester it may show a dead short, but can be higher due to the resolution of the meter.

This should get you started anyway.

Regards.
 
Hi,

Line - Neutral 0.00 Mohms
Line - Earth 0.00 Mohms
Neutral - Earth 0.00 Mohms

I have unplugged everything in every room, and the boiler is on a spur from the ring which i've knocked off. Cooker is on the ring, but i knocked that off too. (As I type I realize the extractor is on the ring too so i will try again with that disconnected)

I switched off the main switch at the c/u, I disconnected the ends of the ring from the breaker and neutral and earth bar.

R1+R2 is 0.32 ohms
 
Them IR readings are a dead short, looks like someone had a fault and changed it non RCD protected to stop it tripping, or you haven't actually disconnected the cables from the DB.
 
Yep I'm a maintenance guy, so i have a bit of knowledge about electrics and access to meters etc from work. But i'm no domestic electrician.
 
When you did the IR test what test voltage did you have your tester set to? If there's still something connected such as an electronic ballast or TV amplifier if might give you low IR readings due the test voltage exceeding the clamping voltage of the built-in surge arrestors.
 
when u done a insulation resistance test did u remove the cables from the consumer unit ?
i see it hard to believe that u didn't have a problem before u moved it to the RCD side ? also like others have said have u removed all items from the sockets and isolated all spurs ? plus is there any neons on the circuit what could give u false readings ?
 
L/N/E all shorted together? Could be I suppose. Or is the OP mis-reading the tester and actually seeing an infinite resistance reading? Daz
 
Hi chaps , first post so hello to everyone.

One explanation could be a neutral to earth fault and the tester is picking up a reading through the connected load.

Not all switched spurs are double pole and can leave the neutral connected in which case if there was a neutral to earth fault then it will show up on L/E test as well.

Could be a problem with the boiler or maybe a some lighting taken off the ring through a spur somewhere.

Regards
 
Hi All,
Had another crack at it this evening

Tryed to be systematic, so identifyed one outgoing cable's conductors as L1, N1 and E1 using tape, other obviously is L2, N2 and E2
Checked the end to end resistance of each conductor on low ohms
L1 - L2 0.27 ohms
N1 - N2 0.27 ohms
E1 - E2 0.42 ohms

Then IR tested between L, N and E again.
L - N 0.00Mohms
N - E 0.00 Mohms
L - E 0.00 Mohms

As suggested then tested the same conductors using the low ohm setting.
L - N 28.8 ohms
L - E 30.1 ohms
N - E 0.14 ohms

Worrying figures, theres a short somewhere i think.

So next i split the ring, I disconnect the socket at the top of the landing, making two radials and from the DB i test each radial

L1 - N1 >99.99 Mohms
N1 - E1 >99.99 Mohms
L1 - E1 > 99.99 Mohms

L2 - N2 93.1 Kohms
N2 - E2 0.41 ohms
L2 - E2 93.2 k ohms

So my Cable 2 leg holds the fault, what do you guys think seems most likely from those readings?
 
Now you will have to narrow it down by dividing that leg , and testing as you do so , until you narrow it right down to one leg between 2 sockets , the fault could well be at one of the sockets ..
 
Had one of these on Monday, split the ring until I was able to identify 1 link between 2 sockets with an almost dead short L - E and on another link a IR reading of 0.35 N - E. Happy days. These things take time and I was doing this in a converted barn where the circuit was not laid out logically so it took a while to trace the links!
 
from the figures you have given, it looks like a N-E fault/short. as said above, keep splitting the faulty leg down.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring Main Tripping RCD, Line to Earth reads 0
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
JimmyB1988,
Last reply from
telectrix,
Replies
30
Views
4,434

Advert

Back
Top