schedule of inspections/supplementary bonding

Discuss schedule of inspections/supplementary bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

pushrod

On page 3 of schedule of inspections (where you put a tick, X or N/A in the boxes), presence of supplementary bonding conductors appears twice - once in fault protection 1) automatic disconnection of supply and again near the bottom of the page under Additional protection. Have looked in the OSG but still unsure as to the differences between the two.

Can anyone explain the differences between the two and give any examples as to when the supplementary bonding means you tick one box and not the other.:confused:
Cheers
 
for the first one, this is basically earthing that is required to achieve automatic disconection of supply (i.e bonds to exposed conductive parts)

for additional protection, these are put in place when the disconnection time cannot be achieved... for example, you would install extra Supplementary bonds to pipework in a bathroom if the resistance between a CPC in the bathroom light fitting or shower circuit is greater than 1667 ohms to the pipework.
 
for the first one, this is basically earthing that is required to achieve automatic disconection of supply (i.e bonds to exposed conductive parts)

for additional protection, these are put in place when the disconnection time cannot be achieved... for example, you would install extra Supplementary bonds to pipework in a bathroom if the resistance between a CPC in the bathroom light fitting or shower circuit is greater than 1667 ohms to the pipework.

Thanks for the reply

So would bonding to a metal back box from a metal socket front would be supplementary bonding to achieve fault protection, ADS ??

And additional protection supplementary bonding is extra bonding between pipework (extraneous conductors) to ensure they are all part of the equi-potential zone and that disconnection times are met???

am i on the right track? must admit to still being unsure.
 

Reply to schedule of inspections/supplementary bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock