Hi All,

A customer has asked for a shaver socket to be installed in his bathroom.

The only issue is that there is no lighting circuit available (loft conversion above and no access to the eaves).

His idea was to come off a socket in a bedroom on the other side of a stud wall to the proposed location.

I'm assuming its a ring final.

My first thought was - yeah - but I'll have to put a fused spur.

Then I thought - wait a minute - shaver sockets are 230 volts anyway - and have their own inbuilt thermistor to trip at only 200mA.

I can't see any regulation or design problem that enforces the need for the fused spur - so I could just run a 2.5mm or even a 1.5mm to it? Its not a fixed load as such, it can't be overloaded.....

Bad practice?
I am wondering what others would do?

I suggested a mirror light with integrated shaver scocket - which are SELV - now that I would fuse down because the light is a fixed load...
 
By an MCB 'or alternatively' an FCU so the MI does give you the assessed choice!
Interesting question, MK has a pdf of the MIs here, they look a bit dated and generic (isolated/non isolated, red-black wires) but presumably they're still valid. It says this about the mains supply..

5. Isolated shaver supply units should be connected to a mains supply protected by an MCB or fuse of 10 amps maximum rating, such as lighting circuit, or alternatively to a fused connection unit that complies with BS1363: Part 4 supplied from a ring circuit.

So it looks like a fused spur is required to meet the 10A protection spec.
But in this case as MV is coming from an RFC then FCU with max 10amp fuse it is.
 
By an MCB 'or alternatively' an FCU so the MI does give you the assessed choice!
True, I was referring to @Marcus Vaughan s application with a 32A protected ring.

Edit:
That pdf link I posted does look out of date so I had another look at the MK site, this one seems more current, a generic instruction set (Wiring Devices Technical) for a range of MK Logic stuff include the Logic+ shaver socket. It doesn't say anything about supply protection but does mention internal protection for the transformer.

@Marcus Vaughan , does that one on the van still have its MIs? Maybe they improved protection on later units to avoid the need for an FCU.
 
Last edited:
If you had discovered that doing an EICR what would you have thought? ……..
Its a spur off a ring circuit so therefore ok? The safety isolating transformer cannot supply more than its design current!

Ive come across this before when doing a bathroom refurb some years back and initial thoughts were that it is wrong but couldn't find anything in the regs to support that.
 
If you had discovered that doing an EICR what would you have thought? ……..
Its a spur off a ring circuit so therefore ok? The safety isolating transformer cannot supply more than its design current!

Good question. Earlier I said it would be a no-code but now I'm leaning towards a C3 - because of the replies above mentioning appendix 15 and those manufacturing instructions.

Ive come across this before when doing a bathroom refurb some years back and initial thoughts were that it is wrong but couldn't find anything in the regs to support that.

I think they'll be a lot of examples of it - but I cannot see any real risk with the set-up.

Does not mean I'm going to do it though - I am going to fuse it down. To ambiguous an issue not to.
 
I think they'll be a lot of examples of it - but I cannot see any real risk with the set-up.

Does not mean I'm going to do it though - I am going to fuse it down. To ambiguous an issue not to.
Good call, the MK sockets have internal protection but it's to protect the transformer from overload, it doesn't help if the transformer fails.

If a fault develops on the transformer primary and it's connected direct to the ring then there's enough power to set it alight without tripping the breaker. MK have mitigated the hazard by specifying max 10A protection.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Shaver Socket from a Ring Final
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
Marcus Vaughan,
Last reply from
Marcus Vaughan,
Replies
22
Views
26,912

Advert

Back
Top