Good morning I was called to a property last Friday where a customer was complaining about getting an electric shock from the shower and taps.
system is a PME
combi boiler so no heating element to check and shower is manual so no leakage on shower.
i have cross bonded all pipe work, when I put my amp meter around the pipe I get o.o87 MA this is 87 micro amps when I touch my voltage tester on any pipe work only 1 prong I get 2 volts but when I put the voltage tester between 2 pipes ie hot and cold cold to shower or radiator to shower I get continuity.
my question is this permitted and ok
 
main bonding intact??? could be static.
 
  • Like
Reactions: 1 person
Sounds like there is something a miss there, if the voltage drops when then upstairs light mcb is switched off, should you not be testing the circuit to see why this is causing voltage on pipework
 
  • Like
Reactions: 1 person
I have had a similar problem in the past do a loop test .could be the incoming neutral broken and everything going thru earth. the dno had to repair the overheads
 
  • Like
Reactions: 1 person
If it's an old house, check if some numbty has taken an earth off the pipework in the loft, for one reason or another. Had that in my sister house before i eventually rewired the house, a bare conductor into a JB on a lighting circuit for a 500W heater in the bathroom. All cables jammed in the 5A JB whose live conductors rubber insulation wasn't up to much after 45 years or so of service.... lol!!
 
  • Like
Reactions: 1 person
Seen that before on lighting circuits with no earth (1960's) earth wire taken from bathroom light/heater to water pipe in the loft and connected by an earth clamp l
If it's an old house, check if some numbty has taken an earth off the pipework in the loft, for one reason or another. Had that in my sister house before i eventually rewired the house, a bare conductor into a JB on a lighting circuit for a 500W heater in the bathroom. All cables jammed in the 5A JB whose live conductors rubber insulation wasn't up to much after 45 years or so of service.... lol!!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shock through pipe work
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
piz,
Last reply from
KAS1,
Replies
9
Views
3,028

Advert