Hey guys , went to a job last night to quote for a new shower install ... After removing the old shower front , I discovered 2 X 2.5mm t&e instead of 1 6mm .. the current shower is 8.5kw and ran into a 40a MCB on RCD side of a split board .. no signs of perished cables or burning anywhere ... Just wandering if ok to go ahead and replace or offer a new circuit in 10mm .. ? .. ps .. don't throw the book at me please haha ..
 
basically you have 2 x 2.5mm cables in parallel. if installed ref.method C, that gives you a Iz of approx 50A, so with a 8.5kW load (36A) Iz>In>Ib. unconventional, bit can't see a problem, asuming that the load is equally shared between the 2 cables. tin hat ready.

edit: what rating shower is being proposed?
 
basically you have 2 x 2.5mm cables in parallel. if installed ref.method C, that gives you a Iz of approx 50A, so with a 8.5kW load (36A) Iz>In>Ib. unconventional, bit can't see a problem, asuming that the load is equally shared between the 2 cables. tin hat ready.

edit: what rating shower is being proposed?
Shower is 8.5kw .. Triton exite plus ..

Thanks ? I just wanted a second opinion as I've never seen it done like that before ..
 
You think they utilised an rfc to supply the shower? Why not run 6mm at the time.

id check there’s no sockets on the circuit as well.

is there an isolator before the shower?

very very strange.
 
If there is an option, I would likely run a new correctly sized cable. This install has questionable ccc due to installation method and cable lengths. And to me it smells like a short cut when it was originally installed. Just my personal view but other than our beloved RFC, any ccc that required 25mm or less should be realised in a single conductor (voltage drop considered separately:) ).
 
i had a full roll of 2.5mm on the van. nearest 6.0mm cable was 40 miles away, and the pub was opening in half an hour. no contest. ???. ( and i did give the customer the readings on a beermat).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Eden electrical

Thread Information

Title
Shower circuit help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
Barrington1990,
Last reply from
telectrix,
Replies
10
Views
2,302

Advert

Back
Top