Been 2nd fixing today, which i've not done for many years. I've noticed that both Volex 13A twin & single sockets have 2 x earth terminals. Is that now standard? I thought that requirement was only applied to sockets that served a lot of IT equipment. Even years ago i would sleeve the earths separately, but then into one terminal. Is there any electrical reason for the change? Thanks
 
Decent sockets with double pole switching, will have 2 earthing terminals. The cheaper single pole switched sockets - which I stay away from, normally have just the one earth terminal.

I personally will use both earth terminals on a newly wired sockets only because it looks better. On a refurb/replacement socket, I'll use whichever terminal is best for the existing cable length.

Earthing of the metal knockout boxes in domestic applications, is of course not required providing one of the mounting lugs is fixed.
 
Well i would personally use one of the socket earth terminals for the rings circuit conductors, and the other for a flying lead to the back box. I don't really care what BS7671 has to say about relying on a face plate fixing screw, i was taught to use flying leads to the back box and see no reason not to continue to do so!!
 
Nothing wrong with flying earth leads inside the boxes - I was taught that way back too. However, back in the old days of the 60's & 70's, you really did need flyleads. Limited use of rcd's and no knockout box grommets was common place - how many original socket boxes from this era do you find without any grommets?
 
There does appear to be a misinterpretation of the requirements for 2 separate CPCs for such circuits.
One conductor run in a ring formation and terminated at separate terminals does not equate to two CPCs.
It needs two separate conductors, each connected to a separate terminal in order to comply.

Im not sure what your saying Spin?
Are you saying the image (for example) in Guidance note 8 page 132 is incorrect!
As it says on page 131 that if the ends of the protective conductor are separately terminated at DB & sockets then Reg 543.7 will be met as shown in image
 
ugh, twisted earths, the bane of fault finding / testing!

You forgot the twisted live and neutrals for extra grief just weakens the cable IMO

Exactly, never have liked twisting conductors together. As an apprentice years ago, it was the norm to twist (was imperial then) conductors together. When metric cables came out, many electricians still twisted conductors together. In my opinion very bad practice. I doubt if many twist conductors together nowdays! Or do they ?

There are people who still do it they should have their pliers confiscated

There are arguments for both.
Twisting together would allow for continuity of the conductors, if the terminal became loose.
Twisting together restricts the number of conductors that can be terminated.
Twisting together is a pain when it comes to testing.

I think people who do are just twisted

i can't see it making any difference what so ever. However, as not in the game as such I just wondered why the introduction. Surly must be more expensive to produce, therefore there must be a reason why. Could it be an EU instruction?

It probably won't make much difference to the Bob's in the factory whether it has one earth terminal or two

EU are not interested in UK sockets....the reason is manufacturers dont have to manufacture both types....cheaper to tool for one only,and the extra cost of the two terminals is sneaked onto us.

The mouldings on a lot of sockets these days universal so they can have one or two earth terminals, the extra cost of the second earth terminal is probably only a few pence

In fault-finding an RFC with a higher-than-expected value for r2, on at least a couple of occasions it has turned out to be due to relying on the socket internal metalwork.

One end of the RFC into one terminal, the other end of the RFC into the other terminal. Screws done up tight. But the sockets had riveted bits of metal work, not always making good contact. I've seen sockets with the best part of an Ohm measured between the two terminals.

Had this a few times I also find the switches can be a bit hit and miss when doing R1 - R2 tests
 
You forgot the twisted live and neutrals for extra grief just weakens the cable IMO



There are people who still do it they should have their pliers confiscated



I think people who do are just twisted



It probably won't make much difference to the Bob's in the factory whether it has one earth terminal or two



The mouldings on a lot of sockets these days universal so they can have one or two earth terminals, the extra cost of the second earth terminal is probably only a few pence



Had this a few times I also find the switches can be a bit hit and miss when doing R1 - R2 tests

Those few pence per socket add up when you are mass producing.
 
Im not sure what your saying Spin?
Are you saying the image (for example) in Guidance note 8 page 132 is incorrect!
As it says on page 131 that if the ends of the protective conductor are separately terminated at DB & sockets then Reg 543.7 will be met as shown in image

That is specifically for circuits that have high protective conductor currents. Which is what Spin is saying.

In the post that you quoted he is saying in a normal RING circuit there is only ONE cpc.
 
Yes i am sure! You may have two ends but its two ends of the same cpc! There aren't two seperate circuit protective conductors! Once again i will totally hold my hands up if i am getting the wrong end of the stick which is usually the case!
 

Reply to skts x 2 earth terminals in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
745
Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Replies
4
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top