I wonder if anyone can help? IM testing a school classroom and they have large sinks with RCd socket outlets above them. I'm sure this isn't right but can't find a reg. Number to prove my
 
You wont find a specific Reg No in BS7671, try looking at Building Regs, it suggests a distance > 300mm from edge of sink and drainer. What are you testing? are you doing a EICR?
 
Last edited by a moderator:
It's not ideal, obviously, but not against regs. As already said, building regs recommend at least 300mm away, but only a recommendation. Unlikely to be a safety issue as RCD protected, but should be a recommendation to be moved imo.
 