Hi all,

After some advice here to settle my mind, is there any regulations to limit the number of sockets on a 20A 2.5mm radial? Reading regulation 433.1 i know it states 50m² floor area, but i can't seem to find anything about the number of sockets? Or is it just the total load that determines this?

The reason is, i have been asked to install some sockets, 10 in total, for means of flexibility of plugging appliances in around the area, I'm being told that the sockets will be used for power tools, chargers, a computer and occasionally a heater.


Any information to help clear this up is appreciated.
 
is that 10 x doubles?

realistically, they're not all going to be used at the same time? or is it something like a school workshop where several people will be working.

There must be a reason they give a floor area, rather than a number of points.... but it'll be down to the installer to know how many points for that area is being silly about it.
 
After some advice here to settle my mind, is there any regulations to limit the number of sockets on a 20A 2.5mm radial? Reading regulation 433.1 i know it states 50m² floor area, but i can't seem to find anything about the number of sockets? Or is it just the total load that determines this?
I think the only reference to 50 sq. m is in informative appendix 15 where it says "historically the floor area served has been limited to 50 sq m". So not a hard and fast rule and somewhat half-heartedly stated even there.
Total load is the main thing.
1 nail gun and a heater could make things interesting on a B16.
Are you at all tempted to do it in 4mm csa, just to leave it more flexible with loading?
 
is that 10 x doubles?

realistically, they're not all going to be used at the same time? or is it something like a school workshop where several people will be working.

There must be a reason they give a floor area, rather than a number of points.... but it'll be down to the installer to know how many points for that area is being silly about it.
Yes doubles. No they won't be used all at the same time, i gather its just for ease of moving around and not using extension leads
 
I think the only reference to 50 sq. m is in informative appendix 15 where it says "historically the floor area served has been limited to 50 sq m". So not a hard and fast rule and somewhat half-heartedly stated even there.
Total load is the main thing.
1 nail gun and a heater could make things interesting on a B16.
Are you at all tempted to do it in 4mm csa, just to leave it more flexible with loading?
Yes 4mm did also cross my mind and possibly the better option i guess
 
As above, you can put as many sockets on as you want. The fact you can does not mean you should!

Really it comes down to expected use/load. If most are phone chargers, etc, then 10 doubles sockets are no big deal, but if a large area than a RFC makes more sense, or going in 4mm radial, so 32A MCB is reasonable.
 
As above, you can put as many sockets on as you want. The fact you can does not mean you should!

Really it comes down to expected use/load. If most are phone chargers, etc, then 10 doubles sockets are no big deal, but if a large area than a RFC makes more sense, or going in 4mm radial, so 32A MCB is reasonable.
Yea I understand that, since posting this and seeing the feedback I am favouring the 4mm radial, it is not a large area that it will be covering, I have been told there won't be any heavy loads its just the ease of having sockets in different locations. Thanks for your help ?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Sockets on a radial circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
Stephen-d,
Last reply from
mydigitalhome,
Replies
28
Views
22,853

Advert

Back
Top