testing a property there, the sockets were wired in black rubber 2 core with bare stranded earth coming into the boxes. Done all the Ring tests and everything was fine, continuity between all conductors and R1+R2 fine also. Just wondering is it safe because you got the 2 core cable without a cpc within the cable?
Do you have any pics?
If it is traditional VIR it will be 60+ years old and while some of it looks fine, other parts with different environmental exposure might have failing insulation. It is possible for the rubber to harden and crumble away leaving exposed conductors, without affecting the IR test result. So it is now considered good practice to recommend replacement even if the test suggests it's fine. The separate CPC is technically a non-compliance if it is too small for a single unenclosed conductor.
Separate earth wire would need to be a minimum of 2.5mm2 if mechanically protected, or 4mm2 min. if not. No problem with the cpc not being part of the supply cable, but this stuff is from the '60s at best. Time it was gone.
What I initially put down was that it was testing fine but that the cable was old and would recommend upgrading. I’m always unsure when I come across a type of cable I’ve never seen before. House was built in 60s so it must be in from then, lighting circuit has no earth also
There was a paragraph in approved document p saying VIR cable is past its operating life and should be replaced, nothing specifically in bs7671 but id struggle to give it less than an FI and would want to inspect every inch, probably bi annually, in practice, with the other issue you mention it sounds like it needs a rewire
Reply to Sockets wired in black rubber query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Hello everyone, hope all are well. I'm changing a ceiling rose and have lost the diagram showing where everything was connected (to the old light)...