testing a property there, the sockets were wired in black rubber 2 core with bare stranded earth coming into the boxes. Done all the Ring tests and everything was fine, continuity between all conductors and R1+R2 fine also. Just wondering is it safe because you got the 2 core cable without a cpc within the cable?
 
Do you have any pics?

If it is traditional VIR it will be 60+ years old and while some of it looks fine, other parts with different environmental exposure might have failing insulation. It is possible for the rubber to harden and crumble away leaving exposed conductors, without affecting the IR test result. So it is now considered good practice to recommend replacement even if the test suggests it's fine. The separate CPC is technically a non-compliance if it is too small for a single unenclosed conductor.
 
  • Like
  • Agree
Reactions: DPG and loz2754
Separate earth wire would need to be a minimum of 2.5mm2 if mechanically protected, or 4mm2 min. if not. No problem with the cpc not being part of the supply cable, but this stuff is from the '60s at best. Time it was gone.
 
  • Agree
Reactions: loz2754
What I initially put down was that it was testing fine but that the cable was old and would recommend upgrading. I’m always unsure when I come across a type of cable I’ve never seen before. House was built in 60s so it must be in from then, lighting circuit has no earth also
 
There was a paragraph in approved document p saying VIR cable is past its operating life and should be replaced, nothing specifically in bs7671 but id struggle to give it less than an FI and would want to inspect every inch, probably bi annually, in practice, with the other issue you mention it sounds like it needs a rewire
 
It's not unusual to come across sections of this kind of cable, several inches long, where the rubber insulation has completely disappeared, leaving just parallel bare copper wires. IR tests absolutely perfect, because dry air is a very good insulator, but hardly safe.
 
rip it out,weigh it in, replace with pvc/pvc.
 
  • Like
Reactions: suffolkspark
agree 100%. I wouldn’t feel comfortable if I knew this type of wiring was in my house
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Sockets wired in black rubber query
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Welsh_sparky_21,
Last reply from
Welsh_sparky_21,
Replies
11
Views
2,242

Advert