Has she got a isolator between meter and board. If so she still has a means of isolation, along with mcbs (although not dp). Then do as suggested lock out mains on board (in on position). Then see what happens.
 
Hi, I have just checked a MEM 2000 unit i have,the RCD has a RED SWITCH ! which is the same colour as the main switch. I think your customer may have been on the sherry ?:rolleyes4:
 
Did u test between the two circuits for erroneous connections.. The live on one lighting circuit could of by mistake got connected onto the second circuit.. Do u no what i mean?
 
Hi all sorry for not replying last night it was my boys birthday so I was out,.
It tripped again twice last night and these were the photo's she sent me.
On the first time everything is off except the rcd ! and the second just the main switch.
I reckon it could be the daughter as she was near the downstairs toilet (where the cu is) both times, customers not having it mind!
Please tell me it's not me being thick this is impossible isn't it.
Also I never mentioned when I did the eicr I tried to find out which circuit it was I swapped one at a time all the circuits onto the rcd side and they all functioned normally for me.
Thanks for all your replies.


IMG_1124.JPGIMG_1123.JPG
 

Reply to Strange fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
419
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
958
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock