What would the rating be for a substation fuse and has anyone ever seen one go while on a job? Had a mate asking me this earlier, and now i feel interested.

As i understand it goes: substation fuse > DNO fuse > CU?
 
Depends on the size of the dno transformer. This is protected by Hv fuses in the transformer switch fuse. This in ground mounted gear. Overhead is a bit different with a number of pt's being protected by oh fuses. Lv distribution fuses need to grade with the Hv fuses, you don't want an Lv fault taking out an hv fuse and the entire sub. Lv fuses can vary between 100A and 630A
Yes I have heard them operate. When you have replaced one and a fault on the Lv feeder makes the tx rumble and grumble until the fuse operates. I have also banged them in onto a fault. You want safety glasses on for that!!! 400A onto a dead short makes a big bang
It should be primary circuit breaker-pmr-oh hv fuses- switch fuse- Lv feeder fuse- etc
 
Last edited:
Have a look at Low Voltage Switchgear & Feeder Pillars | Schneider Electric UK

As mechelec says it’s fun (not) replacing a fuse on to a fault, where people come unstuck is by pulling the fuse back out rather than wait for the fuse to blow safely. Pulling the fuse causes a tremendous arc and probably an explosion. PPE is essential, a colleague of mine was badly injured by a short on a circuit protected by a 1200A ACB. His sight fortunately was saved by his glasses, his face and hands were a mess.

The transformer isn’t exactly happy while this is going on. One particular fault we had was caused by the checker plate over a cable trench being dropped edge on, on to the transformer tails, it blew the plate 6’ in the air.
 
Thanks both of you, i was expecting something along the lines of "Don't ask silly questions". HV/DNO looks interesting, i'm looking at going down that route soon hopefully!


I would recommend it. I have worked for a DNO for 4 years now after various other electrical and mechanical maintenace type jobs, installation, testing etc over a good few years. I find the the work is interesting and you can work towards the authorisation level you want to acheive. It comes with regular pay and the usual big company benefits.
 
I saw an overhead line come down once 33kv took 2 pole fuses but didnt take the third,arcing all over the place anyway rang dno who panicked as it was on a main rd and lots of oh lines so they didn,t know which one it was,anyway guy calmed down quite a bit when i told him i was a sparks,they sent out fire service and asked me to supervise incident till they arrived,which they did 3 hours later and it was early hours of new years day,wish I had got paid for it lol
 
Yeh right. Supervise? Show them there it is maybe.
The first to tell you where to go would be the fire brigade if you tried to interfere! They arrested my boss for sticking his oar in.
As far as I know blow out fuses are used up to 11KV only.
 
Last edited by a moderator:
I wouldn’t want to see one go, I damn near jumped out of my skin when an 11KV blow-out fuse went. Dread to think what a 33KV would be like.
 
well thats what they said it was 33kv,and as regards fb apparently they were told to take advice from me by the guy at the dno,personally I,d rather have been in a warm bed than stuck outside but round here you just get used to helping out.
 
The DNO would not ask you to do anything other that keep out of the way. If they had and anything happened their --- would be in a legal sling.
The fire brigade are trained to do the shuffle walk. Are you? If you don’t know what the “shuffle” is, read up on ground voltage gradients. It looks comical but it is a lifesaver, fatal if you’re a cow.
The last time I saw an 11KV line come down there were 6 dead cows dotted around and nearly a dead farmer if he hadn’t been stopped approaching them.
 
I've only ever heard 3.3kv motor fuses go. That was an experience.

A couple of brushes had gotten stuck to the slip ring, flames everywhere. The cb downstream of the fuses failed to operate.

Was only there because we were having trouble with the excitation voltage.
 
We had a 3.3 motor that the brush gear failed regularly. Saturday afternoon used to be like a kids Easter egg hunt with us searching for bits blown out of the motor inspection cover. It took me 6 months to get the company to agree a new ring cleaning regime, after that no problems. First time it went I was stood next to the ACB when it tripped, it lit the room up. (Didn’t do me a lot of good either).
 
11kv DOEF's sound like a shotgun going off above your head. A "Close to possible fault" instruction always makes you twitchy when you can't see why they operated in the first place
 
yes tony i am trained actually also i was a volunteer with the major incident support team at our local fire station for over a year,dont know why you seem to be getting wound up over this could it be someone has done something you haven,t perhaps?
 
About 10 years ago I was on a commercial job n we lost a phase.i knew it was in this subbie tucked away in a lane as I happened before.pointed the s&s lad in the right direction.he brought out this fancy current meter which clamped into the contacts of the j type fuse to measure the overload n then it shut down.i certainly wouldn't have stuck my hand in the subbie that's for sure.interesting stuff.best explosion witnessed?a 6000a acb feeding busbar trunking with every phase n neutral shorted to earth on the panel for the sake of 2foot of grommet strip!!!where was I? The other side of said panel!i think I got a suntan of that one.
 
About 10 years ago I was on a commercial job n we lost a phase.i knew it was in this subbie tucked away in a lane as I happened before.pointed the s&s lad in the right direction.he brought out this fancy current meter which clamped into the contacts of the j type fuse to measure the overload n then it shut down.i certainly wouldn't have stuck my hand in the subbie that's for sure.interesting stuff.best explosion witnessed?a 6000a acb feeding busbar trunking with every phase n neutral shorted to earth on the panel for the sake of 2foot of grommet strip!!!where was I? The other side of said panel!i think I got a suntan of that one.


Sounds like a fusemate. On a LV feeder fault these units are used in the place of the fuse. You fit an approriate size fuse in it, fit it on the Lv feeder stalks and it closes by remome control via a keyfob. It has a vacuum bottle type circuit breaker inside and saves having to bang fuses in onto a fault like the good old days. If the fault has cleared you then have to remove the fusemate and fit the fuse carrier and if you are quick and lucky the fault will not reoccur in the time it takes to remove the fusemate and replace the fuse.
 
Never used one, but seen them in action. Look a nice bit of kit. Anythings better than shove the fuse in!

http://www.kelvatek.com/fusemate.html


Thats the one. I know someone who forgot to pull the trigger in (which opens the internal breaker) and put it onto a feeder with a fault. It blew holes in the contacts on the fusemate oops
Have a look at the rezap. they are even better as they can be left on the feeder for intermittant faults and autoreclose up to 5 times before locking out. Good on faults because you can press the close button repeadedly to clear a fault (or blow the cable in half).
 
Last edited:
Good on faults because you can press the close button repeadedly to clear a fault (or blow the cable in half).

Good fun!
I think the best was a high resistance fault so a CAT trace was useless. Hours spent faffing about finally got to me, sod it copper links instead of 450A fuses, 1200A ACB as back up. Closed the switch and the ACB held in. The fault blew clear alright, it blew a tree clean out of the ground! Didn’t take a lot of finding after that. The roots had grown around a load of joints on the site of a former substation that had been moved, over the years the tree had been moving the joints.
The switch made a strange dull thud sound when I closed it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Substation Fuse
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
23
Unsolved
--

Advert

Thread statistics

Created
linuxthefish,
Last reply from
Knobhead,
Replies
23
Views
14,042

Advert

Back
Top