My customer needs bigger than 60A supply. Currently BS1361 60A. 4 bedroom house, 4 kids, new circuits..
Before I started in the place it came up at 72A (with diversity), and after my 2 new circuits I am 79A (with diversity). PME, nice condition, modern supply cable, Ze 0.27 so should be able to take 80A fuse).
Given the additions, however I look at it and use diversity I need 80A.
Since I'll be inspected on this job (Mr NICEIC etc), I am sure this needs to be shown to be all ticked off OK. The quote from SSE is £131.42+VAT to upgrade the fuse. Surely all they are likely to do is confirm Ze, check the supply cable and earthing conductor, and change the fuse. (modern cable and 16mm main earthing conductor).
Is this a typical quote? I haven't told the customer yet but he's not going to like it given that in his eyes he gets nothing for it.
Is someone here now going to tell me that they just change the fuse anyway without informing DNO? DNO never seem know what the fuse rating is anyhow when I've asked them before.
Justin
Is someone here now going to tell me that they just change the fuse anyway without informing DNO?
they have installed this BS1361 60A either because they didn't have an 80A on the van or they did it knowing more money again for company in years to come YOU CHANGE IT to 80A £40 you say its got a modern supply cable same as any other.
"just put my tin hat on" :army:
and ye DNO wont like it cause they haven't got there £131.42 +vat
You can be evil at times E54
Had similar issues as you the other day apart from it was a 7.5kW supply. Was told by the DNO system planner that everybody has a 'right' to a 15kW supply but their standard supply is 80A.
Two guys came out on Monday and altered the cutout position and meter positions, fitted a four pole isolator (econ 7), upgraded cutout to 80A and was told that the max charge would be around £70 if they bothered to charge!
The DNO's do know what fuses are fitted and do know what the earthing systems employed are at individual properties. They will come out a couple of times to change the cutout fuse free of charge before they suggest you apply for a supply upgrade.
Personally I think the dangers of peeing off the local DNO boys by unauthorised alterations far outweighs the benefits gained from keeping them sweet
Please do, I am
Sounds like they did a stellar job