This isn't for central heating really this is for a project
Can I switch a 2 port valve like bellow .I.e is the "Switch line" 230v?

MCB >>> Junction box >> Line, Neutral, Earth >>> 2 port valve
........................................>> Line split to Light Switch >>> Connected to SL/Orange of 2 port valve.
 
If you mean a normal spring-return central heating valve like the Honeywell V4043, yes, the control input is 230V, it's just a small 230V motor. Note the colour code though; 230V on brown and blue opens the valve. Once open, the internal microswitch connects grey and orange together. There is no need for a permanent line feed unless you are using the microswitch to trigger something else, in which case PL goes in on grey and the valve will make orange live once open.
 
Thanks for the Reply
So just connecting Brown and Blue to a plug with open the valve?

I thought orange was the SL? and this would need a live connection.
 
Just connecting Brown and Blue to a plug will open the valve?

Yes. (and earth, preferably!)

Orange is the switched line out of the valve that normally controls the boiler / pump. The valve energises the orange when it is fully open, like a relay. When multiple valves / zones are in use, all the orange leads are paralleled so that when any valve opens, the system fires up. The brown control inputs that open the valves in the first place remain separate.
 
Stupid me Orange is switch line out

Sorry I'm not really up on S and Y plan so what does grey do? This is a permanent live and Brown is the input Switch Line?
 
See post 2!
 
What's the application?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Reading
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Switch 2 port Valve with Light Switch...........for project only
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Mark Wright,
Last reply from
PEG,
Replies
9
Views
1,361

Advert

Back
Top