A
Andrewr3
Found a ring main fault today. I was doing the testing after adding a socket on a spur. The signs of a problem started with open circuit on the ring neutral and then a N-E insulation resistance measurement that took just a little longer than usual to settle. But things had changed after deciding to double check appliance on the ring was isolated. I was sure I had ring continuity earlier. I finally found the fault in a switched fused spur to a washing machine. One of the ring neutrals connected into the load side of the switch, and the load neutral was where the leg of the ring should have been. It had been like that since the property was built in 1996. If the washing machine isolator switch was on then the ring sort of worked OK, but when it was off all was not well.
Two months ago in the same property I did a direct replacement of a DSSO on the same ring that had an overheated (charred) line (live) connection terminal. My first thought today was the was the overheating was caused by overload on the broken ring. But of course it could not be because the line ring was always OK. The only common factor between the loose terminal on the DSSO and the mis wired 13A Fused Spur was the installer in 1996.
Two months ago in the same property I did a direct replacement of a DSSO on the same ring that had an overheated (charred) line (live) connection terminal. My first thought today was the was the overheating was caused by overload on the broken ring. But of course it could not be because the line ring was always OK. The only common factor between the loose terminal on the DSSO and the mis wired 13A Fused Spur was the installer in 1996.