Domestic RCD tripped and wouldnt reset cause was a blown low energy light bulb.:D
There you go now for yours !
 
Re: Tell us about your faults !

here's one for ya i just recently went to a property where every time the iron was used after an half hour sometimes an hour and then sometimes longer the main RCD would trip after much testing found to be the surge protection socket on the computer
 
Re: Tell us about your faults !

recently taken out and replaced a 3036 cu board, done all dead/live test procedures everything fine. customer phoned to say whenever they turn the switch off and then back on again at the switched fused spur connected up on the ring connected to the boiler it trips the rcd. been back out redone all tests checked all cable connections and usual busbar connections all in right place. if the spur switch is left in the on position when the rcd is switched back on the circuit is fine its only if the switch is switched off then back on again, all readings in the live tests are ok. any ideas would be appreciated as you know what its like. customer says its was ok before you changed the consumer unit!!. cheers
 
Re: Tell us about your faults !

How many types of cable can you fit in a meter, lead sheath, VIR, T+E, I Peed myself laughing when I saw this, the customer didn't get why lol:D

photo-92.jpg
 
Last edited by a moderator:
  • Like
Reactions: 2 people
Re: Tell us about your faults !

How many types of cable can you fit in a meter, lead sheath, VIR, T+E, I Peed myself laughing when I saw this, the customer didn't get why lol:D

View attachment 5804

I once knew a fella that ran a 3ph machine in his shed. He used his phase then pinched the other two off his neighbours in henly blocks. Time served EITB spark as well.
Absolute bloody genius!!!
 
  • Like
Reactions: 2 people
Re: Tell us about your faults !

Just checked out a small job,customer having cutout moved on tuesday by the local supply company
When checked the sevice found to be pme but then found that there was over head supply Comming in that changed it to TT
Problem is sevice is bonded neutral to earth and also a earth electrode but no Rcd ?

Lost
 
Re: Tell us about your faults !

well i had my rcd tripping continously but then i found that there was a loose connection on the cable tied to the mother inlaws metal chair it was close but fixed now !!
but i got this foul smell coming from her room any ideas!!!
 
Re: Tell us about your faults !

thanks buddy did not think of that solved it now she,s smelling a bit but i suppose they are all like that at thier age
 
Re: Tell us about your faults !

Guy in the unit next to me asked for some help. He was having a problem with the main trip that kept tripping. A 'sparks' had wired up his 9.7kw water heater via a new piece of 6mm , that went in to a switch, came out in 4, then hidden out of sight into 1.5 and into a 6amp trip. Hidden on top of one of the kitchen cupboards was the instructions, which said many helpful things including something about 45 amp breaker!!
 
  • Like
Reactions: 1 person
Re: Tell us about your faults !

Got called out to a house where: they were getting shock from shower while standing in the bath, the rcbo for kitchen circuit constantly tripped out, and some lights glowed a little even when switched off.

On investigating inside CU I found I had no voltage between L & E, although still had 240 between N & E and L & N. In the end I concluded that I had a live incoming earth (TNS supply)! Seemed to me this had to be the result of 2 faults on supply side - one to break the earth continuity back to sub-station, and one nearer the property to connect the live supply to earth - otherwise sub-station fuse would have blown.

I disconnected earth, put in earth rod an connected up as temporary TT, and told customer not to touch the earth until DNO had been as I couldn't think how I could disconnect it. Just glad I hadn't touched the earth as it was live back to sub-station fuse!

btw - DNO did find 2 faults - one each side of the front garden wall
 
  • Like
Reactions: 3 people
Re: Tell us about your faults !

Got called out to a house where: they were getting shock from shower while standing in the bath, the rcbo for kitchen circuit constantly tripped out, and some lights glowed a little even when switched off.

On investigating inside CU I found I had no voltage between L & E, although still had 240 between N & E and L & N. In the end I concluded that I had a live incoming earth (TNS supply)! Seemed to me this had to be the result of 2 faults on supply side - one to break the earth continuity back to sub-station, and one nearer the property to connect the live supply to earth - otherwise sub-station fuse would have blown.

I disconnected earth, put in earth rod an connected up as temporary TT, and told customer not to touch the earth until DNO had been as I couldn't think how I could disconnect it. Just glad I hadn't touched the earth as it was live back to sub-station fuse!

btw - DNO did find 2 faults - one each side of the front garden wall

I have a simmilar one but its only 95v between N and E

DNO have "checked" it but that will be a set of drummonds and said as its a TN-C-S they cant see andy chance its there fault.
 
Re: Tell us about your faults !

Heard of one or two that were tnc-s with the n-e link missing inside the cable head

Did they check that?
 
Re: Tell us about your faults !

Found these beauties at a “Special School”. The company which carried out the installation went bust last year. We were too expensive for the original install but not too expensive to rewire it all….lol

00001.jpg

00002.jpg

00003.jpg

00004.jpg
 
  • Like
Reactions: 2 people
Re: Tell us about your faults !

Not so much fault, as terrible design in the first place...

Was taking apart an old installation as part of rewiring using the same light switch positions etc. Couldn't work out the two-way switching for the landing as live and neutral were brought to both 2-way switches... in the end I traced it out as:
L to L1 of both switches
N to L2 of both switches
light fitting connected between the commons of the two switches.

Functionally it worked, but of course it meant that in one of the 'off' configurations both pins of the bayonet fitting were live! Fortunately I was working all this out with the circuit off.

Was this just a bodge by someone, or was there ever a time when this was an accepted way to do 2-way switching?
 
Re: Tell us about your faults !

Not so much fault, as terrible design in the first place...

Was taking apart an old installation as part of rewiring using the same light switch positions etc. Couldn't work out the two-way switching for the landing as live and neutral were brought to both 2-way switches... in the end I traced it out as:
L to L1 of both switches
N to L2 of both switches
light fitting connected between the commons of the two switches.

Functionally it worked, but of course it meant that in one of the 'off' configurations both pins of the bayonet fitting were live! Fortunately I was working all this out with the circuit off.

Was this just a bodge by someone, or was there ever a time when this was an accepted way to do 2-way switching?


It’s called the “Carter system” and this method of wiring has been outlawed since 1923 for obvious reasons as you have found out. The Americans used to be very fond of it. Proving that they are mental!
 
Re: Tell us about your faults !

It’s called the “Carter system” and this method of wiring has been outlawed since 1923 for obvious reasons as you have found out. The Americans used to be very fond of it. Proving that they are mental!

1923?!? I didn't realise what I was replacing was that old!
 
Re: Tell us about your faults !

Now here's an old one.

The make is 'Revo', and the only info I can find on the web is some info dating back to the early 50's, it's certainly the oldest one I've ever come across.

Also, the twin & earth used in the ring final was blue sheathed!!!. The light was VIR singles with cloth sheath and not a cpc in sight.


Anyone have anymore info on this unit???


Cheers.
 
Re: Tell us about your faults !

I have seen those C/U before and yes the 50s is right, lots of council properties used them and schools and garages, not sure about the cable colouring though that is odd unless it was a local council specificiation
I have seen older than this
much much older
in the old days you had 2 consumer units on for the 5A lighting circuits with a fuse inside and an external lever like a circuit isolator and another for the 15A radial circuits
often wired in then metal tube as singles
I still have my old training manuals in the attic I might have to scan them up and post them here for a laugh, they might even be useful
I have also seen a pre war system with fuses in the neutral and live supplies and big screw in fuses horrible horrible
 
Re: Tell us about your faults !

I used to work for a big company well work may be too strong a word for it lets say I was there every day, well they had loads of these 4 inch fans for kitchens, control rooms loos print rooms etc and the damm things used to fill up with fluff
I found a very very quick way of cleaning them
simply get a CO2 extinguisher from our stores that is due for recharge and shoot that through it
the safety officer said its a bit irish but i cant fault yer logic as you cant start a fire that way and it makes sure the ext company do recharge them and not stick a label on them
mind it was funny when my boss had just cleaned his car and I shot half a tonne of fluff all over it, but this method leaves no DNA so to speak by the time he worked out it had coem from the fan I was having a cuppa and the extinguisher was resting in the corner
he thought the fan had unblocked itself??
then they got rid of me but thats another story
 
  • Like
Reactions: 2 people
Re: Tell us about your faults !

I have seen those C/U before and yes the 50s is right, lots of council properties used them and schools and garages, not sure about the cable colouring though that is odd unless it was a local council specificiation
I have seen older than this
much much older
in the old days you had 2 consumer units on for the 5A lighting circuits with a fuse inside and an external lever like a circuit isolator and another for the 15A radial circuits
often wired in then metal tube as singles
I still have my old training manuals in the attic I might have to scan them up and post them here for a laugh, they might even be useful
I have also seen a pre war system with fuses in the neutral and live supplies and big screw in fuses horrible horrible


Now you mention it, I have seen the units you describe....large black units with a lever on the side & ceramic fuses. Also have come across the old wooden units with the fused neutrals.


It was an ex council property by the way.
 
  • Like
Reactions: 1 person
Re: Tell us about your faults !

it just occured to me that these older fuseboards contain asbestos!!!
you need to dispose of it correctly when you replace the unit
if you click this link you can downlaod free a data sheet
do it properly and you will live to a ripe old age
do it wrong and its not a nice way to end your life as I have seen with older sparkies and plumbers
https://www.electriciansforums.net/attachments/a33-pdf.120214/

the site also gives guidance on other asbestos related items
 

Attachments

Re: Tell us about your faults !

Had a good one today.

Called to a domestic property to install a switched spur in a pool plant room for a pool cover.

Try to isolate the plant room ccu, cant, even with all the (un-labbeled) mcb's off. Work out that it is fed straight from the henly blockes, via a 6mm swa that had made of into an adaptable box, with just the red and black cores coming through a 20mm hole in the box, not double insulated. The sub-main was not protected by an mcb!?!

So, i install a 2way ccu with rcd main switch and a 32amp mcb for the circuit, also put in 25mm tails and 16mm g/y from blocks.

Then i procede to carry out my tests. 0.002M ohm between Live and Neutral!! I know the must be a join somwhere because when the cable leaves it is 2 core and when it arrives at plant room its 3core. I come to the conclusion that there is proberly still i load connected. Tracing the cable back from the plant room i see it goes in to the kitchen, under the kickboards. I find a ccu behind the units, you can just about get into it.

Open it up and find what must be where my cable joins. 2core feeding the rcd main switch, with an earth which is 1.5 or 2.5 coming from the armouring (cant see it though, units in way). No swa's glanded in correctly, just stripped back.

My 3core is connected straight in the load side of thr rcd main switch, yellow core to the earth bar. Also out the load side of the rcd is a 6mm single feeding a 32amp mcb of a cooker. Again no swa's properly glanded.

Im going to re-wire a swa from the ccu installed straight to the pool plant room. Not to sure what to do with the old feed which is still supplying the cooker though???

Ive got pics but ot sure how to up-load them?? on my i-phone. DIY at it's worst.

Sorry about spelling and punctuation.
 
  • Like
Reactions: 1 person
Re: Tell us about your faults !

Here's something I found yesterday. Went round to a house to size up what was required to run power to the end of the garden, and went to have a look at Consumer Unit to check spare ways available etc.

Looking in the well used cupboard under the stairs found the meter in this condition...

2011-06-16 13.08.11.jpg

...lower cover missing, and no obvious sign of it fallen down the back.

Decided I would put some strips of insulating tape across the live terminals as a temporary measure. As I did that, the live tail to the CU fell out! At least it wasn't the live from the supply...

Tightened all the terminals, covered with tape, and told the owner to call the DNO!
 
  • Like
Reactions: 1 person
Re: Tell us about your faults !

Hi all, I have come across a light switch fed to L1 from the board. L2 is the switch live (blue) to the ceiling rose (brown), so must be a JB somewhere. This is on strappers to another switch and all works well. However I need to get a feed to another 2 way light switch, any ideas please?
 
Re: Tell us about your faults !

Here's something I found yesterday. Went round to a house to size up what was required to run power to the end of the garden, and went to have a look at Consumer Unit to check spare ways available etc.

Looking in the well used cupboard under the stairs found the meter in this condition...

View attachment 6122

...lower cover missing, and no obvious sign of it fallen down the back.

Decided I would put some strips of insulating tape across the live terminals as a temporary measure. As I did that, the live tail to the CU fell out! At least it wasn't the live from the supply...

Tightened all the terminals, covered with tape, and told the owner to call the DNO!
Why didnt yopou just ask if they had the cover as they probably took it off to get their free supply
 
Re: Tell us about your faults !

I've finally gotten around to investigating a bit of my new house and found a few minor* faults

1. Spot the fault!




2. Now, I know CPCs are all joined together at the CU, but when they're separate radials for electric heaters and bonded together, surely that's bad practise!




3. These wires were just randomly left in from when the previous electrical heating system was de-commissioned... well, at least that's what I thought:






It turns out that one of them was disconnected at both ends and just laying freely in the ceiling of the ground floor kitchen. So when I was pulling on it, it just kept coming and coming and well, it just fell out:




I decided to investigate, from the main consumer unit, which circuit was which so in pulling the fuses, found that the yellow 20 amp circuit was for a decommissioned immersion heater, which is long gone but the circuit was still live and in a switch plate, screwed in to a double gang metal back-box shared with another switch, which was for one of the electrical heaters that are no longer used either (this circuit was not live).
Then It came time for pulling the fuse for one of the 30A circuits... Oh, I didn't think that was supposed to happen...: !






Now, these are probably all boring faults to you, but they amused me.
I'm looking forward to re-wiring my house once we're married and have the money to do so.

My Main earths and bondings are little on the small side too:





*In my view, all faults are potentially serious, but you know what I mean.

Just straighten up that earth going to the bonding clamp and your NIC DI assessment will be fine buddy !
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Tell us about your faults!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
2K
Unsolved
--

Advert

Thread statistics

Created
kung,
Last reply from
Admin,
Replies
1,591
Views
298,344

Advert