Re: Tell us about your faults !
Wat is that for ?
Wat is that for ?
Got called out to a house where: they were getting shock from shower while standing in the bath, the rcbo for kitchen circuit constantly tripped out, and some lights glowed a little even when switched off.
On investigating inside CU I found I had no voltage between L & E, although still had 240 between N & E and L & N. In the end I concluded that I had a live incoming earth (TNS supply)! Seemed to me this had to be the result of 2 faults on supply side - one to break the earth continuity back to sub-station, and one nearer the property to connect the live supply to earth - otherwise sub-station fuse would have blown.
I disconnected earth, put in earth rod an connected up as temporary TT, and told customer not to touch the earth until DNO had been as I couldn't think how I could disconnect it. Just glad I hadn't touched the earth as it was live back to sub-station fuse!
btw - DNO did find 2 faults - one each side of the front garden wall
Not so much fault, as terrible design in the first place...
Was taking apart an old installation as part of rewiring using the same light switch positions etc. Couldn't work out the two-way switching for the landing as live and neutral were brought to both 2-way switches... in the end I traced it out as:
L to L1 of both switches
N to L2 of both switches
light fitting connected between the commons of the two switches.
Functionally it worked, but of course it meant that in one of the 'off' configurations both pins of the bayonet fitting were live! Fortunately I was working all this out with the circuit off.
Was this just a bodge by someone, or was there ever a time when this was an accepted way to do 2-way switching?
It’s called the “Carter system” and this method of wiring has been outlawed since 1923 for obvious reasons as you have found out. The Americans used to be very fond of it. Proving that they are mental!
I have seen those C/U before and yes the 50s is right, lots of council properties used them and schools and garages, not sure about the cable colouring though that is odd unless it was a local council specificiation
I have seen older than this
much much older
in the old days you had 2 consumer units on for the 5A lighting circuits with a fuse inside and an external lever like a circuit isolator and another for the 15A radial circuits
often wired in then metal tube as singles
I still have my old training manuals in the attic I might have to scan them up and post them here for a laugh, they might even be useful
I have also seen a pre war system with fuses in the neutral and live supplies and big screw in fuses horrible horrible