K
kung
Hi ALL
Just thought id put this one up for all those faults we find.
heres one to kick it off !
Domestic RCD tripped and wouldnt reset cause was a blown low energy light bulb.:D
There you go now for yours !
Re: Tell us about your faults !
I think the guy that did this just liked mixing up all those pretty colours ... Actually, he just used flex cord for everything, including the 2-way lighting, with the CPC standing in for LIVE. I liked the CPC snipped off on the RHS, and the unguarded live bus, lack of bonding, and .... and this supplies a pool :cry_smile:
Reactions: 1 person
So finally decided to do the tests on my house now that my meter is calibrated.
Ring Final is fine (it's a shame) except there is no end-end continuity of the CPC, so it's not fine and yet at all of the sockets I didn't find any issues with CPC connectivity, meaning it could be a break between a pair of sockets. Grrr. Maybe I can convince my wife that ripping it out and starting again is the best approach. (It'll be far easier).
I suppose I'll have to do an end-end of each individual socket. Man I wish I had a wander lead...!
Interestingly though, most of the sockets in my bedroom are spurs from somewhere... that's another investigation job for saturday.
Can't you connect CPC to it's respective Live (leaving other L and CPC unconnected from board) then go to each socket in turn and check L to E there. Then repeat with the other CPC and L connected at board.
Had a fault where a lighting MCB had operated and would not reset. Everything looked hunky dory in the D.B. and within the light fittings. Then, I remembered that my first boss had said always to check if there are external lights on the circuit first if it is a lighting fault. I went outside and found 2 bulkheads with the cabling enclosed in PVC Conduit. Directly adjacent to the one bulkhead was an inspection bend in the conduit which had a partially damaged lid that would definately let rain in. When I removed the bulkhead cover, the water poured out and revealed soaking wet and previously shorted Line and Neutral connections.
Even better, the boss wasn't expecting it rectified until at least lunchtime and it only took an hour. Even better, the customer was his ex-wife so she took great enjoyment in making bacon butties for me and my mate to eat whilst we put our feet up and watched the clock tick. I've learnt to appreciate those moments, they seem few and far between!
Hi,
Im having a bit of a problem with a job i recently went to look at for a friend. The problem was that when the shower was turned on the lights through out the house started to flicker. The shower is also very old and im nt sure what kW the shower is or the cable size due to only having a quick glance at the job. The house is an old house with an old consumer board with mem memera fuse carriers. i would not have an awfull lot of experience with this old boards but im assuming 1st off the shower is drawing to much power, and being so old also has no rcd protection. Is there anyone with any advice as to what could be the problem?
Don't know if this is the right section for this.
I was called to a job simply to add an outside socket. Came off the ring and then tested the circuit. The house had recently been rewired so i presumed there would be no problems.
After opening the front of the CU i couldn't find any ring circuits...ALL individual wires into each MCB. My first thought was they all must be radials.
Nope...Both the upstairs and downstairs rings had been wired into 2 different 32A MCB's.
I've seen some bad wiring in my time but not something so basic on a new install, i was shocked.
I know the firm who did the work and all I can presume is it was an apprentice who wired the CU up.. but that wouldn't excuse the fact the work wasn't checked. Should I report them to NAPIT who they're with, or speak to the owner.
What do you think?
Probably right...i'll give the owner a call. It had made me alittle angry to see such blatent incompetance, but like you say the bloke who owns it might not have a clue. Thanks
In keeping with the theme of this thread...I did recently see a gem of a fault when ripping out before a rewire last year. An electric fire must of had a fault previously and damaged the line wire into the fire. Instead of replacing the damaged cable with a PVC cable or flex...he had used a Steel wire which you use to suspend things from etc and just wrapped it up in insulation tape.
Reactions: 1 person
Got called today to look at an immersion heater in a flat in a 70s build block. Went to test Zs, and the MFT wouldn't take a reading - checked voltages and found earth floating at 23v above neutral! Went back to fuse board in flat and found the same.
Went to meter cupboard downstairs, located the correct SWA supplying the flat in question (the design appears to involve the armouring and all the metal conduit and trunking providing the earth path back to the incoming supply) and found:
...armour visible, and no electrical connection between the gland and the armour. When I pulled down on the cable...
It appeared to me that the SWA had probably never been properly terminated, so quite possible the flat in question had been without an effective earth connection for 30+ years!
Upon clamping the armour properly in the gland, Ze (or should that be Zs?) at the fuse board in the flat fell to 0.08!
Reactions: 6 people
first of all I would start by measuring the voltage at the main isolator in the consumer unit, check the connections are secure ( they are often loose)
check the voltage with everything switched off on the incoming side from the cutout/meter
230/240 v it will vary a little
then switch the light on and see how much voltage drop is occuring and record it ( should be nothing)
then operate the shower and measure again
if the voltage stays more or less the same plus or minus 4V then repeat the test on the switched side of the main switch from the neutral bar and the copper bar feeding the fuses ( if you can access it safely)
if the results are the same the problem lies further on
it could be a loose connection withing the fuseboard
or it could be the lights are spurred of the shower or the shower is spurred of the lights???
not unusual but lethal
you really need to see how the shower is fed from the isolator switch follow the cable along
often the old fashioned MK1 eyeball is the most efficient method
if the voltage drops of alarmingly on the first test, then its the supply cables either loose undersized or possibly the supply cable to the house failing, I have also seen the cut out fuse loose ( it should have screws and nuts to pinch it up)
but thats a supply company problem
stick some pics on here it you like
Reactions: 1 person
on rewiring my lounge (finally) fi.ding annoying and naughty (by todays' standards) things.
also, how many different types of masonry does one house need?!
Sent from my GT-I9100 using Tapatalk
naughty naughty
no grommet for the cable leaving
the CPC should be feed to terminal block first for the fitting and then looped to the back plate
wires are ok in the safe zone just a bit of a bodge
with an attic hatch above it would have been easier to drop down
as fas as masonery it depends on the bodgers and whats handy
I recently found concrete used to patch studwork walls!!
and that bodge dates from 1958 when the house was built, the house had pre made studwork walls, you slotted into place, and you were supposed to drill the timber at top and use a rod to force a gap into the cardboard cells for the cables
this lot used a sledgehammer by the look of things and then used concrete to infill
that took soem digging out for a rewire???
Following a recent Consumer Unit upgrade last year. We had two mcb trip events for no apparent reason. The last trip was accompanied by a smell emanating from the CU. I ordered a new mcb. As I went to fit it, I noticed that the pair of wires were charred, and came out of the terminals by hand!
Reactions: 1 person
Tell us about your faults!
Australia
kung,
Admin,