Testing a rcbo at db or end of circuit?

Discuss Testing a rcbo at db or end of circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
9
Hi Boys,

Just wondering if you guys could clear something up for me.

When testing a rcbo or rcd I would always test from the end of the circuit, for example a socket on a radial circuit.

However was talking to someone recently who told me they test from the load side of the rcbo or rcd at the db. Just wondering if this is ok to do?

I suppose it would save a bit of time walking back and forth from the db to the circuit under test if you performed the test at the db but not sure if it would be allowed or if the reading would be different from carrying the test out at the end of circuit side.

Thanks in advance.
 
Yes you can do this just watch out for MEM memshiled 2 ones you have to put a short peace of wire on them to test them or they will not operate with tester

Yes, you need to do the same for some wylex ones aswell. You put a piece of 10 mm in a connector and then the connector on to one of your probes. Then you can reach the neutral in the rcbo.
And it is recommended that you test as close as possible to the rcbo, rcd.
Jay
 
The MEM Memshiled 2 RCBOs will not operate with the tester if you test them at the DB. There was a thread on this while back explaining why this happens. The way around it was to connect a short peace of cable onto the RCBO and test from the end of it or just carry out the test at any part of the circuit But in answer to the OP you can test at the DB.
 
Yes you can do this just watch out for MEM memshiled 2 ones you have to put a short peace of wire on them to test them or they will not operate with tester

Yes, you need to do the same for some wylex ones aswell. You put a piece of 10 mm in a connector and then the connector on to one of your probes. Then you can reach the neutral in the rcbo.
And it is recommended that you test as close as possible to the rcbo, rcd.
Jay
Or use one of these ;)
 

Attachments

  • IMG_20140214_185808.jpg
    1.7 KB · Views: 143
Yes, you need to do the same for some wylex ones aswell. You put a piece of 10 mm in a connector and then the connector on to one of your probes. Then you can reach the neutral in the rcbo.
And it is recommended that you test as close as possible to the rcbo, rcd.
Jay

Interesting, never had any issues testing Wylex RCBO's or RCD's at the board!

- - - Updated - - -

Are you testing the rcd/rcbo or the circuit?

Because he is just testing rcd/rcbo and there is no need to test the circuit because you have already done at least a zs

??????
 
Interesting, never had any issues testing Wylex RCBO's or RCD's at the board!

- - - Updated - - -



??????

One of the poster's stated they test rcd at furthest point.

This doesn't seem necessarily, as long as the other values from testing comply then it will not fail a properly functioning rcd/rcbo

After all we are only checking they trip in a certain time frame
 
As Risteard states above, but also note that the manufacturers also recommend testing at their RCD device's terminals as well!! This is especially the case when officially recording RCD's values on test reports such as EICR's etc.... You're not testing the circuit, you're testing the RCD itself!!
 
Hi Boys,

Just wondering if you guys could clear something up for me.

When testing a rcbo or rcd I would always test from the end of the circuit, for example a socket on a radial circuit.

However was talking to someone recently who told me they test from the load side of the rcbo or rcd at the db. Just wondering if this is ok to do?

I suppose it would save a bit of time walking back and forth from the db to the circuit under test if you performed the test at the db but not sure if it would be allowed or if the reading would be different from carrying the test out at the end of circuit side.

Thanks in advance.

The object of the exercise is to test the RCD or RCBO so why the hell are you testing the circuit??? :30:
 
The object of the exercise is to test the RCD or RCBO so why the hell are you testing the circuit???

Technically correct but Im just a lazy sod who finds it easier to test at the socket using my plug tester thingy that goes on the end of my cables! Unless of course I get a reading I dont like ......
 
As long as all the loads are removed from the circuit you can test the tripping times OF THE rcd/rcbo at any point of the circuit, as stated its easier to just plug the tester into the most accessible socket to test the RCD/RCBO tripping times but for a lighting circuit it easier to test at the DB
 

Reply to Testing a rcbo at db or end of circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock