Well apart from working on a live board, drilling and connecting loose cables which is illegal as it was possible to isolate..
the circuit breaker you mentioned could not handle the fault level - old C50s are only rated at 4.5kA - so would not have operated safely anyway.
The design was wrong and the routine PIR should have picked this up. If that board had HRC backup protection, the fault would not have been so great and your injuries may well have been less.
So the company and your super are guilty on two counts, unsafe installation and negligent live working.
HSE will have a field day! I'd hate to be defending.
Mike