Davido

Hi Folks,

I have a question about a property in Spain and its power supply

I think I have messed up with my electrical company and asked them to supply me with a lower potential than I require. The house did have a 12,000 KW supply, I asked for a night rate and in order to get this I had to opt for a different power connection either 10,000W or 6500W. I assumed that the 6500W would be per phase I am thinking now it is 6500W in total.

The day they changed the meter the oven started tripping the RCD, the hob also trips it.

Is it usual for an RCD to trip but not latch down just to trip the power? It can be reset by toggling the switch.

Would not having enough power in the one of the phases cause the RCD to trip?

The bumer is if I have to ask to get the higher 10,000W rate I will have to have the house certified again. Is there any way that all three phases can be used together to give me more power?

Thanks in advance
 
Rcds only trip on a earth fault, ovens are always doing this because of the elements could just be unlucky and it happen when it did ?

If you only have 6500w available then that's only about 30amps depending on your voltage ie 6500/230 = 28.26amps and if it was spread over 3phases then you will be in big trouble wouldn't you?
 
Thanks, what gets me is that the RCD does not fully trip, the button does not come all the way down. any clues ? Yip big trouble, that is why I posted here. The RCD also trips on the hottub and hob when it starts drawing around 12 amps. never noticed it on the oven or hob untill I bought a new element for the hot tub thinking that was the cause.

If RCDs only trip on earth faults being under supplied with power on a resistive load should not matter.

I shall call the company back that changed the meter just in case their is a fault there, I am wondering if they have programmed it correctly.
 
Some rcd's trip to mid position to allow you to tell its tripped and not been turned off, as said before they only look at earth leakage and i suspect one of the elements in the oven is showing early signs of failure... get an Electrician in to check this out, if it trips after a time of the oven been on the fault may not show if elements are tested cold it may be the case it only faults when the element is hot and slightly expanded.
 
Are you sure these are rcd's and not rcbos ? is this the main switch you are talking about or for one circuit ? did they fit it when doing this work ? give more details please
 
If you have a 12kw supply, this would be 4kw per phase as it is here in France. However if you have not balanced the various circuits equally between the phases and have one phase that is exceeding the 4kw limit, then the whole system will trip out.
 
That's one thing you guy's in UK don't have to worry about, you get up to 100A on DNO supplies for domestic installations straight off the bat so to speak. In most of Europe and a good few other countries, you pay different rates for different supply KW values. I wonder how many households in the UK could get by on a max 12 KW supply (espeacially over a 3 phase install) or less?? Not many, the dammed 10.8 KW showers would be a killer straight away!! lol!!
 
If you have a 12kw supply, this would be 4kw per phase as it is here in France. However if you have not balanced the various circuits equally between the phases and have one phase that is exceeding the 4kw limit, then the whole system will trip out.

--- so if you have 6500 kW that would be a setting of 10A per Phase. In France the setting in AMPERES is on the disjoncteur de branchment - I would have thought this would be the same in Spain.
 
--- so if you have 6500 kW that would be a setting of 10A per Phase. In France the setting in AMPERES is on the disjoncteur de branchment - I would have thought this would be the same in Spain.

So what are the supply values/bands in France, that you get to choose from, for typical domestic installations??
 
Hi,

About power installed and your evaluation and RCD tripping.
Warning:
- The installed power capacity and maximum power absorbed simultaneously for any premises there are separate and different things.
- About RCD please take a picture for me if you don’t mind.
Probably burned actually.

Thank you.


bertt. :rolleyes2:

 
Davido - From the meager information you have given I am guessing that what has happened here is that when you contracted for your supply to be down-rated to 6500W, the power company has come along and fitted a new control circuit breaker which for your supply size would be a 10A TP&N (an ordinary circuit breaker, not an RCD) This is why your higher rated appliances are tripping, This circuit breaker (or ICP) is the way that they ensure you can only take the amount of current you are paying for and is perfectly normal in Spain.

You need to alter your contract with the supplier back to 12k (15A per phase) or even higher.
 
What sort of property do you have in Spain? I have an apartment which is only single-phase and have no problem with regards loading other than when all the heaters and cooker is on, then it trips on overload rather than earth fault.
I'm not aware of many homes in Spain having 3-phase!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Three phase RCD tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Davido,
Last reply from
WilcoxElec,
Replies
20
Views
6,662

Advert

Back
Top