We just moved to a new house, we brought a chandelier with us. It has the same 15 x 40 watt bulbs as the last house.
There are two switches for this light, one downstairs is a dimmer switch.Upstairs is a rocker switch.

When the chandelier was hooked up, power turned back on and switch engaged with full lights/not dimmed, the dimmer which was rated at 600 watts blew out in about 45 minutes.

I removed the blown dimmer switch downstairs. The dimmer switch was connected to three wires; a black wire coiled around another black wire and a red wire.

I installed a new dimmer rated at 1100 watts. The black coiled wire to common and the other two as runners. When the breaker was flipped back to power on the dimmer switch blew out immediately.
I thought maybe I wired it incorrectly so I bought another of the same dimmer 1100 watt switches and confirmed how it was supposed to be wired and did so. This time when I turned on the power at the breaker, nothing happened. The dimmer switch, when switched to the on position, did nothing. When I switched the upstairs rocker switch the dimmer immediately blew out.
I checked the upstairs switch to be sure it was wired correctly. It also had a coiled wire around a black and red wires.

I then replaced the downstairs dimmer switch with a regular rocker switch, when the power was turned on it flipped the breaker right back off.

first picture is of the wires at the light
second picture is of the downstairs switch wiring
last two pictures are of upstairs wires

Any thoughts?
 

Attachments

  • 20201027_161118.jpg
    20201027_161118.jpg
    76.5 KB · Views: 18
  • 20201123_204638.jpg
    20201123_204638.jpg
    72.4 KB · Views: 19
  • 20201123_205233.jpg
    20201123_205233.jpg
    96.4 KB · Views: 18
  • 20201123_205406.jpg
    20201123_205406.jpg
    124.2 KB · Views: 16
you must have wired the chandelier wrongly, and created a hot - neutral short, usually by mistaking a switched hot for a neutral.
 
Or it's wired correctly but has an internal short-circuit perhaps from the wiring inside being damaged during the move. That might explain why it worked to begin with, then if the wiring at one of the lamp sockets was under stress or crushed, it shorted out as the insulation warmed up and killed the first dimmer. As the fault has tripped the breaker a few times, it is presumably solid enough that it will still be there and can be found in minutes with a multimeter.
 
Or it's wired correctly but has an internal short-circuit perhaps from the wiring inside being damaged during the move. That might explain why it worked to begin with, then if the wiring at one of the lamp sockets was under stress or crushed, it shorted out as the insulation warmed up and killed the first dimmer. As the fault has tripped the breaker a few times, it is presumably solid enough that it will still be there and can be found in minutes with a multimeter.
Thank you, I will check this and may come back to you to understand more.
 
switched hot is what we here call switched live. a cable that becomes live or hot when the switch is turned on.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Southern California
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Three way switch conundrum, any help would me appreciated.
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Dallas,
Last reply from
telectrix,
Replies
5
Views
1,008

Advert

Back
Top