wannabesparky

can someone please tell me why when you change an old rewireable fuseboard to a circuit breaker consumer unit does it have to consist of a time delay rcd on a tt system? and also what would happen if you didn't put a time delay rcd in?
 
Onsite guide - P24 circuits in a TT system need to be protected by RCD/ RCBO's to protect the circuits.

A 100ma 'S' Type is used as a main switch to protect the whole installation and is delayed for discrimination betwenn the other the RCD's/ RCBO's in the installation.

Hope that makes some sense?

Warren
 
If all circuits are rcd/rcbo protected by a 30mA device, why is there a need to have a 100mA as main switch if others will trip before it?

This ones been debated before and I think that you are right in saying that if all the circuits are protected by an RCD/RCBO to the 17th Ed then it could be just a main switch. Can't remember now what the conclusion was for it without getting the regs book out.


what will happen though if a time delay rcd isnt put in?

If one of the RCBO's trip then you could have what they call on upstream effect tripping the main RCD out and losing power to the whole installation. Don't forget that the main RCD is a higher rating but looking after the whole installation and not just one circuit.
 
A standard main switch with RCBO's or dual RCD,s protecting all circuits is permitted on a TT system, providing the CU is either class II or of an all insulated construction.

Happy days.
 

Reply to time delay rcd on tt system in the Australia area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi I am installing my first tt system consumer unit I understand that I need a 100 amp time delayed rcd main switch but can I use rcbos in line...
Replies
23
Views
3K
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock